I know the Capacitor value- 12.5KVAR, voltage 440V gas
filled, then what is the formula for calculate the
microfarad value for this 12.5KVAR capacitor
Answers were Sorted based on User's Feedback
Explanation:
Q=Reactive Power in VAR
U-voltage at capacitor terminals[single phase]in Volt
frq=frequency[50 or 60 HZ=cycles/second]
Q=U^2/Xcap Xcap=Capacity reactance [in ohms]=1/(w*Cap)
w=2*pi*frequency
Then Q=U^2*w*Cap or Cap=10^9*Q/(U^2*2*pi*frequency) if Q
is in kVAR and capacity in microFarad.
If U is the line-to-line voltage the same formula is good
for three-phases in Y but Q=3*U^2/Xcap for delta connection.
Is This Answer Correct ? | 1 Yes | 0 No |
400Kv,can it be generated?why?
what is a panel board?
HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA
why the neutral of power transformer is always earthed?
how the BDV of the oil will be checked using moterised controled HV SET?
What is the significance of integral controller and derivative controller in a pid controller?
What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?
Dsitrubution transformer minimum IR value
If cvt is most advance & effective(economically & stability)so why not use instead of VT(11 kv & 33 kv)?
In EHV transmission line a neutral grounding reactor is often placed at neutral point of shunt reactors. What is the recommended protection for this neutral grounding reactor? Should I use a fast closing switch to bypass neutral grounding reactor when this protection operates?
Why let through energy not considered for ACB breaker while cable sizing?
What is cable gland,why does use for?