We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
why are maintine power factor 0.99 in Eb line? why are used capacitor bank in Eb line? what is the purpose capacitor bank?
4 Answers TNEB Tamil Nadu Electricity Board,
Proviiding the Dedicated N earth and individual Body Earths ,Finally these all looped /Now my Question :- will it not harm in case of Transformer Fault current flows in Dediacted N Earthing to Looped Body Earthing.
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
What is an 86-P or an 86-A trip
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
actual rated capacity of a disc insulator??
relation between power station capacity and voltage level?
in an ac series circuit there are 30 bulbs are connected in a serial set.what will happen if one bulb is fused and we removed the bulb and reconnect with the remaining bulbs? (29 bulbs). will the brightness of other bulbs increase or not?
If u have Powergrid model question papers Please send to below mail ID rajutheprince@gmail.com
how to diffrentiate between ac & dc motors from a distance
HOW TO TEST THE SODIUM VAPOR AND MERCURY VAPOR LAMP ?
what is the preventing maintenance of transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)