We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
Is This Answer Correct ? | 1 Yes | 0 No |
what is a pilot wiring and whys that called a pilot wiers
how to calculate the multiplication factor in HT incomer trivector meters
9 Answers Dalkia, Getco, Gujarat Energy Transmission Corporation Limited GETCO,
how convert kvar to microfarade? circuit diagram of infrared transmiter and receiver? circuit diagram of Fm transmiter and receiver?
why always electric field is linked with magnetic field???
2 Answers Bhushan Power Steel, NTPC, Tata Steel Limited,
Why ACB is used in LT why not in HT and why VCB is used in HT why not in LT
How can we get electric power from lighting ?
what is work of CTPT in 33/11kv Substation
how can I check HT cable ?
what is meant by directional earth fault and non directional earth fault? describe both.
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
What’s electric traction?
what is hormonics. how it is generated & what are the problem faced by that.