We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the work of trip circuit supervision relay?
can i connect the two phases of scott connected transformer,if not why?
for 500mw power production how many range of transformer set in unit please reply if three transformer use .
What is nyquist contour?
Practical applications of series connected resistances?
can indirect loading be called as phantom loading?
Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.
What is the difference between Derived earth Fault and measured earth fault.How it works.
why we grounding the neutral of a transformer?
Purpose of providing neutral isolation panel for parallel operation of diesel generator
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
What will happen if we do not provide earthing to the newtral of a power system ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)