We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
What is notching in dc machine?
Is there any scope for an electrical engineer in MRF company......
What is the basic difference between AVR and stabilizer?
2 Answers Gujarat Alkalies and Chemicals GACL,
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
why we remove capacitor connection in 3 ph Induction Motor while taking noload test.
PLS MENTION QUESTIONS ASKED IN IOCL INTERVIEW FOR ELECTRICAL EGG??
How to make vector group test of transformer?
The earth pin of some three pin plugs are seen split. why?
Which type of control system is expensive — closed loop or open loop?
IN dc capacitive reactance is??
When One Phase PT Missing (voltage drop ) this time current is zero of This phase(PT Missing Phase) and current is Not Zero of other Phase but PF is always Low That Why
What is neutral earth voltage of transformer and what should be the value
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)