We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the cable size we can use for 11kv and 33kv ?
what is impedence voltage
How many earthings are provided for a 250KVA distribution transformer?
why induction motors are rated at 0.8 power factor.
why ac current do not save
solar cell voltage?
Electrical breakdown strength of an insulating material depends on............?why because?
What could be the problem if two power transformers trip on stand by earth fault at same time
What is Surge arrest? How it work?
speed of an electric wave
What type of tranformer generaly at soft wares like capacity 2000 kva 1800 kva etc iam confused it CT or PT OR distribution tranformer
What is meant by locking of rotor in synchronous motor? Explain me locking in detail?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)