why induction motors are of lagging type and not leading
type
Answers were Sorted based on User's Feedback
Answer / jagadeesh
because induction machines are single exited machines.
but synchronous machines are double exited, in case of
double exited machines pf can be controlled by using field
excitations(pf it may be a lagging or it may be a leading)
| Is This Answer Correct ? | 42 Yes | 11 No |
Answer / iamdon
Induction motor is a singly excited machine.It means there
is no scope of power variation by varying the excitation.So
the nature of power factor is solely decided by the nature
of winding,which is moslty inductive.Thats why Induction
motor has always lagging power factor.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / ankit
this is because induction motors draw a magnetising current taht lags the supply voltage..
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / hema chandra.m
as per electrical rools current leads the voltage in pure
capacitive loads
current and voltages are in phase in pure resistive loads
current is lagging the voltage in pure inductive loads
induction motor is pure inductive load thats why induction
motors are lagging type only not leading type.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sridhar
induction machines are single exited machines.
but synchronous machines are double exited, in case of
double exited machines pf can be controlled by using field
excitations(pf it may be a lagging or it may be a leading)
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / vinay kumar
induction motors draws only lagging power factor because induction takes place between stator and rotor and it draws only magnetising current
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / pardon siabala
becouse in induction motors current lags the voltage.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / s.krishnan
induction motor just like inductive load because its have
more copper windings.so induction motor has lagging type
load not leading type load.
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / k.karthik
because all motors are considered to be inductive loads.so
induction motors are lagging type and not of leading type
| Is This Answer Correct ? | 7 Yes | 16 No |
What is the Power factor of DC Power system ?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
Why sometime i receive GCU fault /Excitation voltage loss in my Generator Synch Panel .
Why carbon brush used in dc motor also why its not used in ac motor?
Upload data by LSMW via BAPI in SAP system.
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
how technical is calculated in 11kv line and lt line
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
why transformers are sometimes kept on concrete benches..?
how vector surge relay works ?
what is the use of expulsition protective gap in 11Kv line.
how choose conductor&depending upon load
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)