For an 100kw generator, only 50kw of load is connected. Will
the generator generate only 50kw or 100kw. If it generate
100kw what happens to rest of the 50kw. What happens if we
connect more than 100kw of load?
Answers were Sorted based on User's Feedback
Answer / kj
The answer above is correct in that the generator will only
generate power as required.
The limiting factor with load above the 100kw in the
example is the power output of the engine. If excess load
is applied the frequency will drop until underspeed
protection shuts the genrator down or the engine stalls.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / balwinder
Any capacity Generator will not generate full power at all
times, According to load requirements it will give power. For
50kW load the 100kW generator will generate 50kW only.
There is no problem if we connect more than rated power in
small amount but it cause over heating of generator.
| Is This Answer Correct ? | 6 Yes | 3 No |
Why r use in the tap changing x' mer.
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
what types of load we get from the national grid? is this capacitive or inductive?
how can a race around condition be eliminated using master slave flipflop?????
what is the difference beteen differential protection and over current protection of an alternator
What is Lockout Relay and what is use of it in electrical installation
If carbon brushes spring tension either loose or tight, what happen on Motor performance During Full load Operation?
what happens when dc generator coupled with cycle shaft.also explain what happens when its loaded
What are the functions of different probes used in cro?
Can I do body earthing of machine by using Cable armour or I have to run another GI wire for body earthing and how many wires I need to run. Is there any rule for this. eartnig
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)