what are the problems are there
if power factor is leading
Answers were Sorted based on User's Feedback
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 3 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 2 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 1 Yes | 0 No |
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
what is meant by Is limiter?what is the use of current limiters in electrical ditribution network?
what is the use of permanent magnet generator in exciter
How much current can 11KV line carry? What are the formulae used to calculate current across both side of transformer? Moreover I need to know can I connect 33KV line with transformer of 1600KVA? Details are: V=415, Pf= .9
when the Transmission and Distribution network where is the "feeder" lines are located? and why should be used in T&D network.....
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION
Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.
0 Answers DAE, Tata Chemicals,
For example, if I use Star delta transformer for distribution, Can I Connect 230 V lighting load bewteen secondary phase & primary neutarl. What will be the effect, if I connect in this manner?
The height to which the liquid in a tank to be maintained for a certain constant velocity?
In any Industry, Which voltage level either 3.3kV or 6.6KV to be chosen? Then I would like to know ,Is there any cost consideration or Rating of motor?
What is UJT PNP, NPN transistor & working principles?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)