When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 3 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 2 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 1 Yes | 0 No |
whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?
why transformer comes only in standard rating like 11kv,33kv,66kv....and not like 33.33kv and so on?
what is the technical term when and alternator's prime mover fails.
pre arcing time of ehv breaker
what is disadvantages of high power factor
how does directional relay work incase of ac ?
if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE AMPEAR PRIMERY SAID
how squirrel cage & slip ring motor works? how they differ from each other
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
how to save the power?
the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.
Explain what happens to the speed of a series motor as the load decreases
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)