When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 3 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 2 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 1 Yes | 0 No |
why for transformer protection we protect tranformer from 3rd hormonics and 5th hormonics and what is the reason of generating these horminics in electrical system?
How to define Kirchhoff current law and voltage law along with simply examples.
if the armature current in a dc generator is ac ( sinusoidal ) why doesnt the sjhape af armature mmf a sinusoidal (ni) ? armature mmf in case of a dc machine is triangular.
In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????
What is the fullform of IPS in substaion using Aluminium Tubes
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker
what are the checks of diesel gensets
What is Single Phasing fault???(not single-phase fault)
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
How does PLC work for sychronising of Two or more DG sets?
can we use ELCB and RCBO in one db
what will happen if any motor runs long time with star connection in400vA.C. system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)