what are the problems are there
if power factor is leading
Answers were Sorted based on User's Feedback
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 3 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 2 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between on line & off line UPS
What is the meaning of transformer 16 / 20 mva.
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
What are the reason of unbalanced secondary voltage of HT transformer 33kv/6.6kv ? Incomming voltage is balanced.33kv each secondary voltage 6.6 kv 6.4 kv 6.4 kv At no load conditions.
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
which relay is used on long transmission lines
10 Answers ABB, Bhel, Student, Tata Steel Limited,
How many types Switchgears?
In case of power/distribution transformer what is percent impedence?
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
how is capacitor bank look like
how could we know the size of cable by physical view?
0 Answers Havells, United Engineering,
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)