I have AC automatic voltage regulator 15KVA
What output currant?
Answers were Sorted based on User's Feedback
Answer / muzamil
if voltage regulator is single phage..in think its out put
I=kva*1000/230=65.21 amps...in full load,
if regulator 3 phage...I= kva*1000/415*1.732*pf*eff
=15*1000/415*1.732*.85*.85
=28 Amps.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / rajkumar
we should convert that kva to kw,
Power (KW) =KVA*pf
=15*0.8
P KW =12.
then,
P=1.732*V*I*COS*EFF
we need current,
I= P/1.732*V*COS*EFF
= 12/1.732*415*0.8*80%
= 17.7 A
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepanshu tiwari
for even 3-phase you don't divide "KVA" by p.f , so the current for 3 phase will be :
i= KVA/(1.713*line voltage)
i = (15 * 1000) / (1.713*line voltage(415V))
= 21.10 A
Is This Answer Correct ? | 0 Yes | 2 No |
What is meant by Resonance what are the different types of resonance and what are uses of them?
What is core CT & it's function?
What is Bolted fault?
Why we are use dol starter up to 10 hp
why do we have another cartridge filled with oil fitted at the bottom silica gel cartridge in power transforers
Find active & Reactive Power transmitted in a transmisston line having Vs30 degree(sending end) to Vr(zero degree)at receving end with line inductance X ohm. Vs(30degree)-------------------Vr(zero degree) X ohm
why we used servo motor insted of inducation motor?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
why voltage will come different in phase?
what is the purpose of vector group in a transformer ? if 2 tranaformers r connected in parallel the vector group is same or not? for parallel operation 2 transformers of different manufacturers maintain same vector group or not?
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
what is the contact resistance of sf6 circuit breaker??