how we convert Mili ampere
to temp txt,level txt,flow txt,pressure txt range value
Answers were Sorted based on User's Feedback
Answer / raja
measurement Milli Ampere - minimum Milli ampere value /
maximum Milli ampere * 100
Example 12mA how mach range tx
12-4 / 16
8/16*100
0.5 * 100
= 50 % RANGE
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / faiyaz ahmad
Hai Mr. charan kumar,
Actually the formulae is:
Range= (Actual value(mA)- LRV/Span) * 100%
Span=URV-LRV
=20mA-4mA
=16mA
So,Range=(12-4/16)*100%
=(1/2)*100%
=50%
Is This Answer Correct ? | 5 Yes | 0 No |
in above answer1 why not max amp value should be 20ma
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abdul rauf
Actual formula is PV (procees variable)-LRV/Span×100%
Range=l2-4/16×16
=50%
And process Varible (ma)=Rang in % ×Span/100+LRV
Ma=50×16/100+4
ma=12
Is This Answer Correct ? | 0 Yes | 0 No |
what is Instrumentation?
What is furnace draft control?
How to calibration of vibration probe
1 Answers Mina Al Ahmadi Refinery,
What is the difference between DCS and SCADA?
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
How do bending tubing provide better measurement than using tubing fittings such as elbows?
What is DCS?
as an instrumentation engineer which are the things we have to know / or we must have idea about that....
i want interview questions about PROCESS CONTROL INSTRUMENTATION , SENSORS AND TRANSDUCERS IF ANY BADY KNOW ABOUT THAT PLEASE SEND TO MY MAIL karumudi1003@gmail.com
8 Answers Honeywell, Reliance,
the 3 most common transmitter protocol being in refinery or qatar gas and aramco.
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?