how we convert Mili ampere
to temp txt,level txt,flow txt,pressure txt range value
Answers were Sorted based on User's Feedback
Answer / raja
measurement Milli Ampere - minimum Milli ampere value /
maximum Milli ampere * 100
Example 12mA how mach range tx
12-4 / 16
8/16*100
0.5 * 100
= 50 % RANGE
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / faiyaz ahmad
Hai Mr. charan kumar,
Actually the formulae is:
Range= (Actual value(mA)- LRV/Span) * 100%
Span=URV-LRV
=20mA-4mA
=16mA
So,Range=(12-4/16)*100%
=(1/2)*100%
=50%
| Is This Answer Correct ? | 5 Yes | 0 No |
in above answer1 why not max amp value should be 20ma
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abdul rauf
Actual formula is PV (procees variable)-LRV/Span×100%
Range=l2-4/16×16
=50%
And process Varible (ma)=Rang in % ×Span/100+LRV
Ma=50×16/100+4
ma=12
| Is This Answer Correct ? | 0 Yes | 0 No |
is here anybody who knows how to calibrate the pressure transmitter? ONLINE
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
why we are using analytical instrument in plant ?
what is the difference between -24 : +24 & 0:24 and where it use?
why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
I am a instrument technician. recently i attend interview and face one of question for DP transmitter ,the client asking about the calibration of DP transmitter ,am answer the calibration procedure, they will ask one more question. why open LP side in atmosphere? i did not answer that question. so please help me and explain the particular question. Dear firends waiting for your valuable replay
3 Answers Qatar Petroleums, Samsung,
what is the procedure to isolate flow a transmitter and flushing it?
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
how to calculate interface capelary level transmetar lower S.G.0.54 and uper S.G. 0.26 and h=490 mm
WHAT IS THE VALUE OF MICRON
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)