Is it possible to convert 4 wire transmitter to convert to
2 wire with additional relay.Please send detial with
drawing,i will appreciate.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
No, it is not possible to convert a 4 wire device (power on
2 wires, output signal on 2 wires) to a 2 wire, loop
powered transmitter.
A 2 wire loop powered transmitter uses 3.7mA of the current
loop to runs its electronics. That's why the 'live zero'
starts at 4.0mA, so that there's some power avialable to
the transmitter's electronics.
There's lots of technologies that cannot run on the limited
power of approximately 3.7mA at 24Vdc. Thermal dispersion
flow meters, most wet cell gas detectors, thermal
ionization detectors, to name a few, which have to be 3 or
4 wire devices in order to have sufficient power to operate.
Carl Ellis
Measure First
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / amit
it's function ablavale in transmitter otherwise we do not
convert them.
| Is This Answer Correct ? | 0 Yes | 5 No |
1.can you use SCADA instead of DCS,DCS instead SCADA 2.Difference between DCS and PLC,can their role be reversed i.e. role interchange 3.Difference between RTU and PLC
1 Answers IOCL, Lakshmi Machine Works,
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
whats the diff b/w zero pressure and obsolute pressure
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
What is modbus?
Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?
WHAT PRINCIPLE OF GAS ANALYSER( CO,CO2,N2)
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
can anyone tell free downloads website for fundamentals and principle of basic pressur,temperature,level and flow
How to measure high frequency using thermistor
What is the use of control cable?
what does 5/2 solinoid valve means?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)