when an eddy current probe is installed inside of a turbine
or compressor in case of probe problem same as:crash of head
of probe,changing the scale factor because of low measuring
gap(physical gap is ok(example=1.14mm)but voltage is
reduced(example=-6 volts),is any way to check the probe,when
the ohm of probe is ok.thank you,(Karim Tavakoli)
Answer / kumar
proximity probe tip is wound on coil if any damage in tip won't get reading. proximity probe installed in -6v gap voltage didn't get proper microns because that time magnetic flux line is not created fully so we installed probe in -10v this time probe 200 microns/mills or 100 microns/mills we get exact variation in probe
Is This Answer Correct ? | 0 Yes | 0 No |
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000
Ple give me "INDUSTRIAL INSTRUMENTATION AND CONTROL S.k. Singh 3th edition" Solution manual to self-Check Quiz and chapter-wise PowerPoint Slides. Home web-site not available... Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Thanks for all...
What is the Differance between Graphics And SCADA Graphics? SCADA Graphics have less access?
In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?
1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?
what is insdustrial vibration.who it works. give atleast 2 types of insdustrial vibration
how to trim the pressure transmitter ?
suppose there is gas flow meter I want to know weather meter calibration is done at high pressure or low pressure? pls justify.
HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
Specify for Cables - Flame Retardant and Fire Resistant?