We have drive feeding an output contactor for a 5000 hp
motor @ 5kV application.
The motor FLA is 629amps x 1.25% service factor = 786.25
amps
The cable that we current have in place between the drive
and the output contactor is 350kcmil- MV-105 (parallel
cables). Per the NEC table 310.60 (C) (69). This show the
cable ampacity is at 615 amps per cable for a rating of
1230 amps.
We have derated the cable for the cable tray and the
multiple cables application and our calculations show that
after the correction factor factor we are at 922amps.
1230 amps x .75% correction factor factor = 922.5 amps.
The customer is driving us to then use another safety
factor of .25% off of the already derated cable. Can you
please provide a longhand calculation for your solution on
this application?
No Answer is Posted For this Question
Be the First to Post Answer
How do u term the word 'OF' in Megger Testing???
calculation of lad carryinc capacity of 6mm2 cross section wire in 415 voltage circuit. What will be the amps.
What is Meant by Load factor in Power plant?
In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?
what is standard height of an energy meter from ground?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
Why grounding is generally done in supply end?
how to protect motor in dol starter having capacity of 30 hp.40 hp?
is the value of inductance depends upon the evalue of thitha in doubly excited machine?
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
why the transformer neutral give to the earth ?
i want to do a project on PLC.... please give me an idea.....