We have drive feeding an output contactor for a 5000 hp
motor @ 5kV application.

The motor FLA is 629amps x 1.25% service factor = 786.25
amps

The cable that we current have in place between the drive
and the output contactor is 350kcmil- MV-105 (parallel
cables). Per the NEC table 310.60 (C) (69). This show the
cable ampacity is at 615 amps per cable for a rating of
1230 amps.

We have derated the cable for the cable tray and the
multiple cables application and our calculations show that
after the correction factor factor we are at 922amps.
1230 amps x .75% correction factor factor = 922.5 amps.

The customer is driving us to then use another safety
factor of .25% off of the already derated cable. Can you
please provide a longhand calculation for your solution on
this application?



We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FL..

Answer / Vijendra Singh

To calculate the ampacity after applying an additional safety factor of .25%, we can multiply the derated ampacity (922amps) by 1 - .25%:nn922 * (1 - .0025) = 922 * .9975 ≈ 918.68 amps.nnTherefore, the final cable ampacity would be approximately 919 amps.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is difference between power transformer and distribution transformers

1 Answers  


1.protection used in transformer ? 2.Why breather called breather ? 3.Working of conservator tank.? 4.Speaker of parliament ?

4 Answers   Power Grid,


now a shunt motor is practically a constant speed motor , then how does it meet the increase or decrease in the load ?

1 Answers  


what happens when a power transformer neutral earthing broken???

11 Answers   MacLellan,


how can we check a fully charged battery?

2 Answers   KSEB,


difference bteween neutral grounding resistor and neutral grounding transformer??

1 Answers  


what is divercity factor?

4 Answers   ABB,


Electromotive force is provided by:(a) Resistance’s(b) A conducting path(c) An electric current(d) An electrical supply source

2 Answers  


why tube light flicks??

1 Answers  


how to improve IR value in HT motors?

3 Answers   ABB, AMW, Macleods,


HI FRIENDS,MYSELF & MY GROUP OF FINAL YEAR ELECT ENGG. ARE MAKING A 50/3HZ,5HP,1000RPM,440V SALIENT POLE SYNCHRONOUS GENERATOR.COULD ANYONE OF U TELL ME WHAT COULD BE THE ADV. & DISADVANTAGES OF MAKING SUCH A LOW FREQN.GENERATOR/

2 Answers  


what is transient earth voltage

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)