how to improve IR value in HT motors?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It is not possible to improve IR value as insulation can not
be injected.You can remove the water contents by heating the
coils by making full load current pass through ,using 3
phase dimmer-stat with rotor locked.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / prem
insulation resistance is measured using megger.if megger shows
meaurable value in tens or hundereds then just change the insulatin of lt motor to improve it.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / k.prakashchandra
With dimmer-stat (auto-transformer),it may not be possible
to get full load current in large motors .Then you have to
use strip heaters for heating the coils or DC supply (no
back emf)
| Is This Answer Correct ? | 4 Yes | 1 No |
On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
if i am in front of transmission line how to know that current direction without any equipment
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
what is the significant for using two types of voltage(line voltage & phase voltage)
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
what is interlocing and what is the purpose of this?
How to conduct the Magnetic Balance test on Power Transformer?
1.Difference between vcb and Acb and partes. 2.Difference between STS and ATS.
What is s-domain and its significance?
In my home i am getting too much electricity bill (more than 4000) but I am very much sure that we are not consuming that much. How i can check this ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)