what happens when a power transformer neutral earthing
broken???
Answers were Sorted based on User's Feedback
Answer / privin p v
according to KCL midpoint of a star connection is zero potential.If the load of the transformer is balanced nothing happen while neutral earthing broken.But in case of any unbalancing occurs there is no way to go the circulating current and heat occurs.It will damage the transformer
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / tejpratap pandey
trnsformer phae to neutral voltage unbalanced & its may
dammage load side equipment.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / r.ramadoss
Netural is providing in the transformer for passing 3rd
assymentrical current , if the netural was not present ,
due to the surge voltage or un balanced voltage the
transformer life time will be decreased
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / anand
harmonics will increase and sinusoidal output will tend to
become a bit nonsinusoidal
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / dk gnfc
When neutral open,line voltage flowing in phase,so overvolage occurs in all phases,and if REF provided,it will trip the transformer as protection against neutral opened from earth
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaraju n
in this condition is un safe condition .
transfarmer is become fail to operation.& become a dameged
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / srinivas
there is a standby earthfault will occur on load side.
| Is This Answer Correct ? | 0 Yes | 6 No |
Answer / thuranga
Normally any power or normal transformers is designed in
such a way that all the three phases will be 99.9% balanced(
winding wise).
so neutral in transformer is not at all needed,but for extra
protection neutral is put.
so if the neutral is not present,there may not be any much
change in its operation but vibration of the transformer
might increase.only that will be the change.
| Is This Answer Correct ? | 4 Yes | 13 No |
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
define B types and C types in MCB ?
why there is no current in the rotor body althrough the flux linking with it also get changes. why current only flows in windinds not in rotor
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?
What are various power system instabilities and what are their effects on power system operation?
what are the disadvantages in GIS over AIS
if u have single phase load (un balance) and the main power cable is 3.5core means netural is .5 of phase and can the three phase current make the return paht in .5 neutral.
how can we calculate that how much capacitor is needed for a system to increase the pf?
practicalLY what is impedence ...?
what is capacitor voltage transformer?? how it is different from potential transformer?
In a running D.G set engine and Alternator is revolving at 1500RPM but no output in the terminal>>>>what to do?? someone told excitation problem ....please advice
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)