one KVAR takes how much amps, and how to add power capacitors
to electrical panels, for example if one of the MCC drawn
800amps means how much KVAR required
Answer / wareagle
Before you can answer this question you must knoiw the load
power factor.
KVAR amps = KVAR/(kv x 1.73) eg 600 kvar 400 volts
600/
(0.4 x 1.73 = 867 amps
To determine tha KVAR required you must know the existing PF
Then you determine what you want the new PF to be before
you can calculate the new PF.
| Is This Answer Correct ? | 1 Yes | 2 No |
what is the meaning of 5% droop or 7% droop in AVR?
why some time Railway Fan not Rotate,But after a small rotation by human then it rotate normally? Why?
Why PT burnts?
What is depreciation factor?
i) in which cases should we go for neutral and where should we go for ground? ii) in domestic supply we are getting 230v a.c.and what is the amount of current?
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
For which purpose the temp. rise test of transformer is conducted?
what is cogging in motors?
where is highest transmission voltage is used in india
why insulators colour is BROWN?
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
why neutral grounding transformer is used for generator and why it is not used for transformers?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)