what is the primary current in 415/415 v when secondry of
dry type transformer is shorted.?
Answers were Sorted based on User's Feedback
Answer / naresh kinger
First calculate the short circuit current on the secondry
side. It will be = FLC/percentage inpedence X 100.
Now you can calculate primary current using tranformer
ratio.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / naresh kinger
It will be 139/4.7 x 100 = 3415 AMP on secondry side.
Since ratio is 1/1, primary current will also be 3415 AMP.
Hope it clear now. For any doubt, you can write me at
n.k.kinger@gmail.com
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ravishankar
flc is 139amps .then impedance of the transformer is 4.07
then it is 34.15 amps.ratio is 1:1
is the primary current34.15?
Is This Answer Correct ? | 2 Yes | 2 No |
For group 1 , 2 whather i have to prepare my technical or general studies etc? and im graduate in ee engg. for wht posts im eligible for? please tell me!
IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace.
what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?
How does a digital electronic meter work??????
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
what is surge impedance loading and it's significant in power system?
what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable
I have 2 Nos of 2500kVA 33/0.415V cast resin transformers. How to decide on ampere rating of HT Panel? Also advise me how many panel RMG i have to consider whether 4 panel ok?
why do you give the dc supply to field of alternator
Explain the operation principle, advantages and disadvantages of the following converters: a) A 12 pulse converter b) A Switch-mode inverter c) A thyristor inverter
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
Why the brushes used in dc machines are made of carbon not from other metal?