On load tap changer (OLTC) explode?
Transformer
Vector group: Ynd11
Rated Power: 353MVA
Rated Current: 693A
Voltage:294/20KV

OLTC
Type: T III Y1000 110/c 12193w
Max Operation Current: 295A
Step Voltage: 550V
Arrangement in Tx windings: Y Connection

Problem: Damage of Unit 1 Generator Transformer On Load Tap
Changer (OLTC)

Description of Incident:
9.00 a.m. :- Generator No Load test on excitation system
started

10.30 a.m :- Carried out AVR change over
test

11.30 a.m :- Preparation for Generator Manual Synchronizing
test


12.00 a.m :- Manual Synshronizing test started.
Observed incoming generator voltage higher than running voltage.
CECR operator operated Generator Transformer OLTC to bring down
the incoming generator voltage

12.03 a.m :-Generator Transformer abnormal alarm operated at
Gen.Control Desk (CECR)
CECR operater at Generator transformer bay informed that the
transformer
oil splashed out from OLTC.
CECR operater informed that he heard explosion inside OLTC.
Observed Oil level & Oil Flow alaram operated at Tranformer
local annunciator.

12.05 am :- CECR operator 'Open Gen Field Breaker”

12.10 a.m. :- Elec1 team inspected the OLTC and found the
OLTC rupture disk was broken
and oil spilled at OLTC area.
- Elec1 found the OLTC top cover bulging.

Do anyone know why and possibility cause happen in this OLTC.

Answers were Sorted based on User's Feedback



On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / mushtaq ahmed

Dear Sir, The OLTC of Generator Transformer should not be operated when Generator is in parallel with Grid. OLTC step change introduces a step voltage difference, which results in very high circulating currents. Generator AVR takes some time to adjust to this new voltage. But by that time, a very high current has flown thru the circuit. OLTCs are not rated for this, especially during changeover.

Is This Answer Correct ?    6 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / k.prakashchandra

Generator voltage is decided by excitation and not by OLTC which is provided on HV side . If the voltage on Generator side ( LV ) is reduced with OLTC ,then the voltage difference will be more resulting in more current due to poor lagging pf . AVR maintains the set voltage if apfc mode is not selected . This happened due to wrong operation of OLTC and loose contacts in OLTC . You could have equalized the voltage operating AVR voltage control .

Is This Answer Correct ?    1 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / jayesh n patel

failure is happend after tap operation , chances of contact stucking in between positions and full load current passes more time through transition resistance( as per design current passes for 60 to 90 mili seconds only, while snape action)and it got burnt ,and voltage has cut with big spark, sudden pressure has develop in side the tank and oil has got expand which result in bulging of top cover and oil spread,(mechanical failure result in electrical failure).

Is This Answer Correct ?    0 Yes 0 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / sakono

May be explode from
1. During moving the OLTC contact, some part was lossen and
OPEN circuit occure.
2. Some material of OLTC was fail and loosen. then the OPEN
circuit was occure in OLTC.
3. Contaminate inside OLTC chamber
4. Oil was contaminated
5. TAP Position of OLTC was not in step.

Is This Answer Correct ?    1 Yes 2 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / jayesh n

 while contact changing if it stuck in between position and if full load current is pass more time from transition resistance than resistance got break and heavy spark has occure, due to which sudden  pressure develope in side the oltc tank and top cover got bulged and oil spread out side the tank (transition resistance is carrying current for short time only that is  60 to 90 miliseconds only, while contact snapping action).

Is This Answer Correct ?    0 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / j.kesavan

oltc always problem,why its opration is motorised in auto
cotrol ,thats why disc breake every time

Is This Answer Correct ?    3 Yes 5 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / sudheer

please check the OLTC inside
connections ,carefully .because some times the connector
plate rollers not touch properly. so the winding temp.
increases continuously and oil will over-heated.

Is This Answer Correct ?    1 Yes 3 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / j.ikesavan

my friend please check your inter lock system how to
working motor on load tap changer your winding failure its
going up and down voltage thats why this disc is breake.

Is This Answer Correct ?    1 Yes 4 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / brad stroh

where did this happen at? what is your location? we
specialize in failure analysis.

Brad Stroh

alineeds.com

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What is double delta conection in AC Motor? And can we done the double RPM of the motor by double delta conection?

1 Answers   vguard,


what is different between synchronous & asynchronous motors

3 Answers  


can we measure +,-.zero sequence current ....? if so how can ???

2 Answers   NLC,


what happen when power factor of 2 parallely operated transformer become equle?

0 Answers   Flextronics,


what is mean by busbar and what is the difference between busbar,transmissionline,feeder,distribution line

0 Answers  






why we did not get shock by touching nuetral of any single phase supply of a electrical equipement?

6 Answers  


n1 =1000 n2 =?;v1 =200:v2 =400

1 Answers   APGenco,


in basic 2 phase will short means tripping the power but spot welding 2 phase shorting but not tripping it will welded why.....(Q)

0 Answers  


what is the purpose of shading ring or shading coil in electrical equipments.

0 Answers   BARC,


how does an centrifugal and screw type chiller will work. which chiller efficiency is high and why.

0 Answers   Hyundai,


How to PLC give the command to electrical

1 Answers  


what is the use of the puls transformer in UPS & how it works???????????

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)