I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel
of 400 kVAR(LT).Now if i want to remove the LT APFC panel
and install a HT(11kV) APFC panel on the HT side is the HT
APFC panel will work same as the LT APFC panel(improve the
power factor),if yes what will be rating of the HT APFC
panel?what is the formula to calculate HT APFC panel rating???
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The power on HT side is equal to power on LT side +
3%(1.6%). The power rating of APFC remains the same.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / kathiravan
Since the PF is corrected "before" the bank is connected
(EX:A--------B---------------C----------------D-----------E.
Suppose If the bank is connected the location @"C",the PF will be corrected from location A to C only,where as location C to E will not be effected by the installation of location C)there wont be much effected weather to locate capacitor either primary or secondary of the transformer.Rating of the capacitor must be the respect of HV/LV supply voltage.
| Is This Answer Correct ? | 1 Yes | 1 No |
can we run AC & DC cables in same tray
What is Lockout Relay and what is use of it in electrical installation
Air circuit breaker safety
What are differences between Voltage, EMF & Potential difference ?
what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then why we are not using in our day to day appliances?please justify the answer
For Electrical / and Electronic Systems, when we say efficiency is 80%, then what happens to other 20% from the Power consumption.? I.e. what happens to this?
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
my b-tech percentage is 50%. what answer will satisfy the hr ?
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
What type of motor is used inside computer CPU.
In Plug used in house,Why Earth of the plug more thicker & deeper?
What is the difference between an insulator and a dielectric?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)