How we can calc. the Backup time of a battery Bank???
Answers were Sorted based on User's Feedback
Answer / karthik raman.b
its depend on current of the load which connected to the battery amphere per hour if a battery having 10AH it can give 10A load upto a hour
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / avinash
First you must know the ampere-hour of your battery bank as
per the manufacture's specification.Now discharge the
batteries as per the C5 rating( for Ni-Cd batteries) or C10
rating (for Lead -acid Batteries).Discharging can be done
by connecting the positive and negative terminals of
batteries to the copper plates and immersing in a salt
solution, which will act as a load. The distance between
the plates can be adjusted to set the discharge current.
Measure the amount of discharge current and time till the
battery voltage of each battery in a bank drops to 1 Volt
if it is a 1.4 volt cell. Now multiply the discharge
current and time. This is the measure of the Amperehour
capacity of the bank.If the Amppere -hour capacity as per
the manufacture is available then you can determine the
percentage capacity of your bank at present.Remember that
charging and discharging of battery bank improves the
health of the battery bank.However, for lead -acid
batteries these cycles are around 750 or say 3 years. For
Ni-Cd batteries the life is around 25years or more if
maintained properly.Selecting a overated battery is also
not adviseable as it won't get discharged completely and
this may result in sulfation of batteries and early death
of battery bank.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sanat ullah khan
Answer
# 1 it depond upon the output load
Thanks for Marking this Answer 0 Krish
Answer
# 2 its depend on current of the load which connected to
the battery amphere per hour if a battery having 10AH it
can give 10A load upto a hour
Thanks for Marking this Answer 0 Karthik Raman.b
Answer
# 3 Hi Krishna,
V HV AN 65AH 32 No's of Batteries connected 60kva UPS,
What will be the full load backup time???
Thanks for Marking this Answer
Answer
# 4 First you must know the ampere-hour of your battery
bank as
per the manufacture's specification.Now discharge the
batteries as per the C5 rating( for Ni-Cd batteries) or C10
rating (for Lead -acid Batteries).Discharging can be done
by connecting the positive and negative terminals of
batteries to the copper plates and immersing in a salt
solution, which will act as a load. The distance between
the plates can be adjusted to set the discharge current.
Measure the amount of discharge current and time till the
battery voltage of each battery in a bank drops to 1 Volt
if it is a 1.4 volt cell. Now multiply the discharge
current and time. This is the measure of the Amperehour
capacity of the bank.If the Amppere -hour capacity as per
the manufacture is available then you can determine the
percentage capacity of your bank at present.Remember that
charging and discharging of battery bank improves the
health of the battery bank.However, for lead -acid
batteries these cycles are around 750 or say 3 years. For
Ni-Cd batteries the life is around 25years or more if
maintained properly.Selecting a overated battery is also
not adviseable as it won't get discharged completely and
this may result in sulfation of batteries and early death
of battery bank.
Thanks for Marking this Answer 0 Avinash
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahesh meshram
Calculate the AH of battery as said above or the given by the manufacturer if is same then ok if not then take actual calculated. If capacity of battery is 10AH and load current is of 10A then it will give back up for 1H
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif_emerson_csm team
Hi Krishna,
V HV AN 65AH 32 No's of Batteries connected 60kva UPS,
What will be the full load backup time???
| Is This Answer Correct ? | 0 Yes | 1 No |
why exciter frequency 150 Hz ?
what is the earth resistance
what is ignition?
For backup batteries connection,which method is best? series or parallel ?
the power loss in an overloaded line is mainly due to? a. resistance b. capacitance d. inductance d. none
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
our plant maximum demand has 500 kva.need to suggest me to maintained pf 0.98.how much capacitor bank will be connect to the supply line.
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
why solinoid coil used in tripping rely?and why not other type coil?
how dc ct works?
what is amf panel & how it is working
why should we place 9KV lightning arrestors in 11KV substation ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)