When we give supply to a transformer 11 kv and we get 415v
from it, so when we give supply to same transformer 415v on
ht side what we get?
and
When we gives supply to any transformer to L.T. side 415v or
220v What supply is on H.T. side?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The same ratio holds good.If you apply 415 volts on LT side
,the voltage on HT side would be 11KV.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / ramakrishna
When we give a supply of 11 KV on HT side and we get 415 V from LT side, the transformation ratio is 26.5(11000/415).
So,
1) If you give a supply of 415 V on HT side of the same transformer then you will get 15.6 V(415/26.5) on LT side.
2) If you give a supply of 415 V on LT side of the same Transformer then you will get 11KV on HT side.
| Is This Answer Correct ? | 5 Yes | 0 No |
What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"
How to operate a ac chilar plant?
How to Convert Gen KW to H.T amps ?
i have to install a HT panel, what components, I have to use in this and what will the diagram of that diagram,please tell me each and everything.
aternator every parts and its working
5. What is PMG in Alternators?
1> what r different types of fault in cables? How will u locate and test these faults? 2> why earth wire is provided on top throughout the transmission line. why not only on towers? How much area it can protect? 3> what r different types of transmission losses? How power loss can be minimized? 4> what is the % of power loss on transmission lines?
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
why 30 ma elcb is used ?why cant 100 ma?
if the voltage across the lamp drops by 1%, the power drawn will be reduced by how many %?
What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)