5. What is PMG in Alternators?
Answers were Sorted based on User's Feedback
The answer above is partially correct. All AC alternators
presently manufactured are brush less type with built in
AVRs ( Automatic Voltage regultors ) Normally AVR get feed
back from load for its regulation. If the loads connected
have excessive harmonic content, feed back to AVR get
distorted and hence regulation gets affected. To avoid this
a PMG is mounted on the alternator itself which feed DC to
armature winding without reference to the load
Is This Answer Correct ? | 31 Yes | 15 No |
Answer / nagendra
To completely eliminate the malfuntion of AVRs(that are
being fed from generator terminals through excitation
transformer) due to load fluctuations on the alternator
Permanant magnet generator is a solution.PMG wil feed to
the AVR giving AC output,which wil be converted into DC and
wil be fed to the field winding of the AC exciter of the
main generator(but not to main generator field).Finally AVR
controls the exciter output (by varying its field
voltage).Exciter output wil be directly connected to the
main generator field through rotating uncontrolled
rectifiers.
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / santosh kumar verma
PMG is Permanent magnet generator mounted at the end of the alternator shaft. The alternator generally uses a self excited generator and converts its voltage to DC and then applies to Exciter armature winding through AVR. Generated voltage from this exciter fed to Main alternator field after proper rectification (Through rotary bridge rectifier) & alternator get excited, This kind of alternators are named as brushless modern alternators.
A synchronous generator whose AVR is taking its input power from the generator is termed a shunt excited generator. If the generator’s terminal voltage is reduced as is seen with transient voltage dips upon the application of significant block loading or motor starting, the input voltage to the AVR is reduced by the percentage of transient voltage dip. This reduction in input voltage to the AVR reduces its ability to force swift recovery of the generator’s terminal voltage, and may well impact the generator’s ability to start relatively large motor loads.
Meanwhile the PMG is used for stability of Alternator voltage, better regulation to make reliable source.
Please note in such system A complete brushless alternator built with the below combination
PMG + Exciter + Main Alternator
Is This Answer Correct ? | 14 Yes | 1 No |
both the answer is right
please tell me ur email ID
my email ID is sanjeet.swarnakar@gmail.com
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / basudeb sarker
The PMG is rotated by the prime mover and cuts the field
windings of the pilot exciter, which induces high frequency
1ph A.C in these windings. This is the starting point of
generating a voltage
This voltage is fed to the AVR where it is regulated and
rectified and its D.C output fed to the main exciter field
windings.
Is This Answer Correct ? | 9 Yes | 7 No |
Answer / nishant chowdhary
answer 2 is much practical and correct.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / asif raza
please anybody tell me why the PMG o/p supply frequency is
taken more then ac generator frequency. plzzz tell me the
reason.
Is This Answer Correct ? | 3 Yes | 2 No |
please anybody tell me why the PMG o/p supply frequency is
taken more then ac generator frequency. plzzz tell me the
reason.
Is This Answer Correct ? | 0 Yes | 0 No |
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
1. transformer design formula ? 2. how to calculate the primary turns and secondry turns ? 3. core types ? 4. how to find the primary current and secondry current ? 5. how to calculate the stacking factor ? 6. range of fulx density ?
2 Answers Automation, Indian Railways, Mogora Cosmic,
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
how can get electrical c licence.now i am working in spining mill , transformer capacity 2750KVA. SANCTION DEMAND 2250KVA. PLEASE ADVISE ME . MY CONTACT NO 09944226823
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
Give idea about General Engineering. From which book i can study this topic. Pl. reply me via email. My email is ravi@bhelhwr.co.in, also give the name of book/website, from where i can prepare it.
Pls tell me what is the exact current conducting capacity of copper and aluminium cables?how much capacity of cables need to 90kw induction motor&how?
why the secondary winding of the transformer is not open circuited ?
5 Answers Nepal Electricity Authority, Torrent Pharma,
Why star delta starter is preferred with induction motor?
what is the ambient temperature of transformer oil & winding?
Define the overload capacity of the motor.