What is the cause for a blown fuse in one phase of primery
side(HV) of a three phase transformer( 4169v-460v) in the
time of closing its supply breaker.
There is no load on the secondery side of the transformer
in this moment.
Answers were Sorted based on User's Feedback
Answer / engr.abdurrahim
As your Question, I think in your transformer is having
interturn fault or single phasing or may be LG
fault.Without load if any fuse blown means connected things
(Transformer)itself having problem.
Solution:
Do the Meggaring and check insulation between, phases at HV
side,LV side,
Check insulation between phase to neutral, Phase to earth.
Check Earth resistance also.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pillay
It could be just high inrush current,
incorrect fuse size or a defective fuse
in the first place.If it recurs than
further investigations should be taken.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / niranjan
Due to high inrush of current or there may an inter turn
fault on ther primary side of the transformer
| Is This Answer Correct ? | 1 Yes | 2 No |
what meant by Locked Rotor Current ?
how to select a capacitor, i mean we use 3.5 mico ferad cap for a celling fan,but how to select a cap for 1h.p motor,etc.........
i want to know how to calculate the battery capacity based on the UPS . ex i want to run have one kva UPS Which should run 10 hours ? in that case how many batteries to be installed and what will be the AH Value .
Why did call copper as a electrical conductor?
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
Why the starting current in Induction Motor is very high as compared to normal rated current ????
What do you mean by transformation ratio of instrument transformer?
how much allowable resistance that can be difference in motor all coils?
What is bus-bar?
how harmonics are generated due to nonlinear load & how harmonic filters work?
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
what happens when power factor leads or lags to electical or home appliances
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)