What is the cause for a blown fuse in one phase of primery
side(HV) of a three phase transformer( 4169v-460v) in the
time of closing its supply breaker.
There is no load on the secondery side of the transformer
in this moment.
Answers were Sorted based on User's Feedback
Answer / engr.abdurrahim
As your Question, I think in your transformer is having
interturn fault or single phasing or may be LG
fault.Without load if any fuse blown means connected things
(Transformer)itself having problem.
Solution:
Do the Meggaring and check insulation between, phases at HV
side,LV side,
Check insulation between phase to neutral, Phase to earth.
Check Earth resistance also.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pillay
It could be just high inrush current,
incorrect fuse size or a defective fuse
in the first place.If it recurs than
further investigations should be taken.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / niranjan
Due to high inrush of current or there may an inter turn
fault on ther primary side of the transformer
| Is This Answer Correct ? | 1 Yes | 2 No |
importance of reactive power management
Why dose voltage rated at 11kva
1 Answers TK Chemical Complex,
Between Turbo alternator and Hydro alternator which one is more difficult to cool and why?
why distribution transformer is uesd in Delta/Star formation?is there any significance in doing this?If yes then breif?
transformer is working or not with supply of DC?
A cylindrical wire is compressed in length by 10%. The percentage decrease in the resistance will be?????
if installing the transformer why put the sprit the stone ?
Give idea about General Engineering. From which book i can study this topic. Pl. reply me via email. My email is ravi@bhelhwr.co.in, also give the name of book/website, from where i can prepare it.
Which oil can be used in transformer?
which one is the most common system for secondary ditibution
Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)