why do we use UPF watt meter in short circuit test of the
transformer and LPF watt meter in open circuit test of the
transformer
Answers were Sorted based on User's Feedback
Answer / pradeepkumar
In full load test, rated current
is made to flow and hence the
fraction of magnetising current
is less compared to the watt
component.. Hence power factor
would be nearly unity.. So UPF
wattmeter is used..
But whereas in no load test,
since the machine is not loaded,
watt component of current would
be negligible as compared to
magnetising component.. Hence
the power factor would be very
low.. So LPF wattmeter is
used..!!
Is This Answer Correct ? | 116 Yes | 12 No |
Answer / abhishek
if you calculate the power factor in the no load test conducted you will get a lower value (.2 to .5). In blocked rotor test or in load test the power factor will be usually higher if you calculate (around 0.7 to 0.8). So we use lpf and upf wattmeter respectively.
Is This Answer Correct ? | 4 Yes | 7 No |
how much current (in MW)can be carried max. through S/C dog & Panther Conductor ?
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
what r the main parts of central chiller plant in Air conditioner ? explain the function of each?
i am completed diploma in ece,and working in ht and lt lines.so is elligible diploma in ece for get electrical C Licence?plse give ur opinion?
Which type of DC generator is used for electric welding purposes and why?
what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?
What is the difference between automatic & semi-automatic star-delta starters?
will there be any problem by recovering slip from single phase induction motors?
electricity bill multiplication factor 487.20xconsumption=total unit in kwh. what is 487.20 ?
How much load with stand the copper cable by sq mm apro..
Why should we use the igniter in the sodium vapour lamp.
7 Answers ABB, Delphi, Mudhra, NTPC, PICT,
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??