why do we use UPF watt meter in short circuit test of the
transformer and LPF watt meter in open circuit test of the
transformer
Answers were Sorted based on User's Feedback
Answer / pradeepkumar
In full load test, rated current
is made to flow and hence the
fraction of magnetising current
is less compared to the watt
component.. Hence power factor
would be nearly unity.. So UPF
wattmeter is used..
But whereas in no load test,
since the machine is not loaded,
watt component of current would
be negligible as compared to
magnetising component.. Hence
the power factor would be very
low.. So LPF wattmeter is
used..!!
| Is This Answer Correct ? | 117 Yes | 12 No |
Answer / abhishek
if you calculate the power factor in the no load test conducted you will get a lower value (.2 to .5). In blocked rotor test or in load test the power factor will be usually higher if you calculate (around 0.7 to 0.8). So we use lpf and upf wattmeter respectively.
| Is This Answer Correct ? | 4 Yes | 7 No |
Single line diagram for dbb (double bus bar)system.
Is there any question in the name of Static Switch in UPS??
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
why are the maintaine power factor and how can this control and this is how work.
Could explain briefly of over excitation in transformer.
What is the permissible value of earth resistance and as per which standard / act / rule ?
definition of transformer
specific difference of ICT&Auto Transformer
0 Answers TNEB Tamil Nadu Electricity Board,
which %age of corona losses increses if frequency is increased to 25%.
3 Answers ADCET, Maihar Cement,
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
Why different types of connection in transformers are used? (star/star,star/delta,delta/star,delta/delta)Why we are only taking in consideration of star/delta type transformers? if only star/delta is good in practice where doses other type of transformers are used? Note: i want to know place of using different types of transformers other than Star/delta type with brief description.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)