Answer / mohan
Formula:1.73 X V X I/1000
180X1000/1.73X415 =I
Full load current 250A.
But we should have take only 80%
| Is This Answer Correct ? | 131 Yes | 20 No |
Answer / santosh jagale.
Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.
If you consider the PF is 0.8 Lag.
Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,
144=1.732*415*I*0.8
I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.
This is the full load current of generator with 0.8 PF &
415V.
In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.
| Is This Answer Correct ? | 52 Yes | 4 No |
Answer / ranjith18
BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)
| Is This Answer Correct ? | 45 Yes | 6 No |
Answer / gins
Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.
W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.
Accordingly select your incomer with suitable kA rating
with respect to your total load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / mubashar ali
I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V
u can also use the fector as mantion Ranjith
I = KVA * 1.4
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / ahmed umar
Since the Genset Rating is given in KVA as 180KVA.
I think you should calculate the full load Amperage as
follows:
Formula
I=KVAx1000/Root3x400V
ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / ashvini kumar meena
People are unnecessarily trying to guess pf. Its not required.
To calculate KVA quantity you just need voltage and current.
Power factor comes into picture when you are talking about
real power(in KW.)
KVA = √3 * V * I
Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=√3 * 240(phase Voltage) and I to be
fount.
Above Mr. Deepak Kapil in answer have solved it correctly.
| Is This Answer Correct ? | 2 Yes | 0 No |
When and where resistance earthing is used ? How to calculate the time constant for earth fault
What are the safeties in elevators?what is the use of governor in elevator?
if we convert kw into Ampers,which one formula use by us,pls tell me?
what is compatible kva for 3300 watts and why
PLC Based Process Automoation Panels?
what is the instataneous value of voltage in a 3-phase balanced star connected circuit?
why power factor occur only inductive load not in resistive ?
Define coil span?
How to calculate busbar size & what is the procedure we make for determine that?
35 Answers Auko Tex, Integra, PowerTech, Shadhin Group,
Advantages of low voltage drive (control panel)
How to determine alternating current frequency?
What OPGW is better than Microwave or PLCC???
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)