three phase 180kva diesel generator can take how much load
in amp and what is formula to get this?
Answers were Sorted based on User's Feedback
Answer / mohan
Formula:1.73 X V X I/1000
180X1000/1.73X415 =I
Full load current 250A.
But we should have take only 80%
| Is This Answer Correct ? | 131 Yes | 20 No |
Answer / santosh jagale.
Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.
If you consider the PF is 0.8 Lag.
Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,
144=1.732*415*I*0.8
I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.
This is the full load current of generator with 0.8 PF &
415V.
In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.
| Is This Answer Correct ? | 52 Yes | 4 No |
Answer / ranjith18
BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)
| Is This Answer Correct ? | 45 Yes | 6 No |
Answer / gins
Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.
W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.
Accordingly select your incomer with suitable kA rating
with respect to your total load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / mubashar ali
I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V
u can also use the fector as mantion Ranjith
I = KVA * 1.4
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / ahmed umar
Since the Genset Rating is given in KVA as 180KVA.
I think you should calculate the full load Amperage as
follows:
Formula
I=KVAx1000/Root3x400V
ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / ashvini kumar meena
People are unnecessarily trying to guess pf. Its not required.
To calculate KVA quantity you just need voltage and current.
Power factor comes into picture when you are talking about
real power(in KW.)
KVA = √3 * V * I
Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=√3 * 240(phase Voltage) and I to be
fount.
Above Mr. Deepak Kapil in answer have solved it correctly.
| Is This Answer Correct ? | 2 Yes | 0 No |
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator
WHY CFL can't made in shape of bulb.
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s
is IS says that neutral should be brought to switch box. and this one is a recomended practice
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage.
difference b/w bus bar and tie line?if possible explain with eg:
A motor works on 30 killo watts.how much ampers will be required if it works on 440volts?
what is the difference between elcb and rccb ?
how can we calculate the reactence of the current transformers?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)