Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we use metering current transformer as protection
current transformer if not why? & if yes why?

Answers were Sorted based on User's Feedback



can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / arun

Selection of CT for protection is majorly depends on the
burden limit and Kneepoint voltage at which the core of the
CT gets saturated,after which it cannot produce the
tripping emf in its core.

So check the burden of CT and kneepoint voltage.

Is This Answer Correct ?    19 Yes 2 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / ranga

because protection CTS are rated for high currents than the
metering CTS, so we should not use metering CTs for
protection purpose.

Is This Answer Correct ?    17 Yes 9 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / felixraj

the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)

protection miss leads in metering CT (it may fails or
nuisance tripping)

Is This Answer Correct ?    10 Yes 3 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / mohammad

Metering and protection CTs have different accurecy class
level as metering CT has 1 class level and for protection
itis represented by 5P,10P etc..

Is This Answer Correct ?    5 Yes 3 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / mohsen khoshsefat

Introduction to Protection Transformers
Protective Current Transformers are designed to measure the
actual currents in power systems and to produce
proportional currents in their secondary windings which are
isolated from the main power circuit. These replica
currents are used as inputs to protective relays which will
automatically isolate part of a power circuit In the event
of an abnormal or fault condition therein, yet permit other
parts of the plant to continue in operation.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?

1 Answers  


how do the stepper motor works.

1 Answers   Vardhman,


1 sq mm conductor=? how many amps

3 Answers  


if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?

3 Answers   NHPC,


what do you mean by earth fault in transformer?

2 Answers   L&T, UPL,


As per BIS, Earth pit resistence value?

4 Answers  


I want to know in body earthing which material can be use either copper plate or GI plate please guide us which is best option.

3 Answers  


1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.

0 Answers  


solor panels arrange some angle,panel is flat fitted energy was produced or not why?

0 Answers  


I use 20 nos led tube 4feet, in pathway 100mtr approximate, so what size cable i use for lighting

0 Answers   Oman Cables Industry SAOG,


we convert 66kv to 33 kv to 11kv to 440v. why can't we directly convert 33kv to 440 ?

9 Answers   EMC, Jakson, L&T,


How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.

0 Answers   Grasim,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)