Answer / sayan
MPCB:Motor Protection Circuit Breaker, which performs the
same function as that of an SFU.
MCB:Miniature Circuit Breaker, It also functions as a short
circuit prevention device. It can be 1,2,3,4 poles
depending on the requirement.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / vinod
MPCB: all the bove full form are correct.
its also an breaker with inbuilt overload protection.
as per the cordination in the panel after contactor OLR is
needed to be provided.if we are using MPCB there is no need
for overload relay.
MCB: Minature circuit breaker.
this limit it is available up to certain breaking
capacity.can be used for lower breaking capacity
| Is This Answer Correct ? | 6 Yes | 2 No |
MPCB : Motor Protection Circuit Breaker.It is protect from
over load,Short circuit & Single Phasing also.
MCB : Miniature Circuit Breaker give protection from over
load & short circuit Only.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / jayaseelan
mcb
thermal overload,sort ckt protection
mpcb
thermal overload,sort ckt protection,olr adjustment
anyother answers welcome...
| Is This Answer Correct ? | 11 Yes | 9 No |
MPCB have selectable range.
MCB has fixed ratting.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / naveen kr.mishra(03-08-1987)
Hi friends, The every answer are correct but no body wrote
about the single phasing protection that is second portion
of Question clearly.
Answer-
MPCB will not protect to motor during single phasing
accuratly.It can do moulfunction during single phasing.
So normally MPCB dose do sufficient for single phasing.
Thanks
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / supreet virdee
Basically MPCB is used to protect motors from malfunctionng
and from overload whereas MCB does not work on three phase,
provides insufficeint protectin by only tripping the
cirrcuit.
MPCB can be used on three phases R,Y,B and provides full
protection to the motor n avoid it from burning.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / atul
The question is still not clear to me......
as.
1). MCB protects from overloadin,short circuit..
2). MPCB protects from overloading,short circuit and motor disconection...in all of the above cases it will trip....nd moreover the main dfrnc btwn mcb nd mpcb is dat mpcb is provided with auxiliary cntacts(normally open nd normally closed)basically mpcb is connected with cntactors to provide two cmponent starting.......nd mpcb ranges r variable it can be set from frnt bt mcb is set for a fixed rating....
| Is This Answer Correct ? | 0 Yes | 1 No |
difference between the applicability of nortons and thevenin theorem
What is the "IS" for Rising Main?
When geneartor is running in poor lagging side power factor its excitation current increases then it is running in improved lagging side.Kindly tell me when gen is running in leading side what will happen
our industries ht line so power fluctation(once drop of power please rectify causes
Which type of DG need Netral Earthing?
how to amps calculate from 1KVA?
How many Cylinders are there in Diesel Generator?
in pf lagging means current decrease by increasing voltage is correct or not ? reason ?
for 644KW load which MCCB should i use
what should be the resistance between two winding. Let 10 kw motor
how much insultion resistance 11kv cable.
what is the function of bearing in dc mchine" and where it is placed
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)