Can we connect two or more energy meters/Amp meters on one
CT set(Three phase).
Answers were Sorted based on User's Feedback
Answer / shariff
More 2 Ammeter/Energy meter can be connected on CT secondary,
provided their burden (VA) rating should be high, otherwise
its accuracy will fall.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / abhishek pathak
ya why not. Actually always current is flow in series you put on one wire from ct s1 and connect on first energy meter s1 and put on one wire from s2 of first energy meter connect on s1 of second energy meter and second energy meters s2 connect on ct's s2. Then your current path become OK and there will be same rating in twice energy meter which is actual. like this all phase CT will connect on energy meter. and make paralleled of phase voltage line on meter.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / abdul whab
i have an ATS panel in which a single breaker will work all the time but i am installing two different CT's on each circuit breaker. can i use one measuring meter for that as at a time only one source will work.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
What is mean by power factor?
18 Answers Shreem Electric Ltd,
What are the three types of compensators?
can transformer develop three phase poer from a single phase source?
what is the acb tripping & closing voltage.
without name plate detail of blower how we can find out the HP & Rpm ? the input voltage is 230v single phase
What is ideal IR values for ground and neutral.
0 Answers Hindustan Power Projects,
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
What is mean demand of the Plant?
which is best ac or dc
Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)