Can 2 transmitters be connected to Integral orifice meter taps? Does an integral orifice comes with 2 set of taps?
Integral orifice plate assemblies are either designed to install as part of the process piping with flange mounts for a manifold valve, or for direct mounting to the process heads of a DP transmitter so that no transmitter piping is required. They're designed primarily for low flows.
Although intended for direct mounting to a manifold valve or process heads, optional fittings are available for high temperature applications that move the transmitter away from the integral orifice assembly. Presumably, fittings for dual transmitters could be fabricated as well.
Commercial orifice flange unions have a single tap on each flange. It would be possible to tap a 2nd DP transmitter into the piping for those taps.
Dual or even triple transmitters on a single flow element and set of taps are sometimes referred to as 'stacked' transmitters. There are commercial adapters for close coupling dual DPs with a special manifold valve from vendors like Century Valve. This has a long history of useage to cover a wide flow range with multiple DP transmitters, each of has a relatively low or limited turndown.
An SIS safety calculation has to account for a single-point-of-failure with a single set of taps.
There's always the possibility of a corporate engineering policy discouraging or forbidding dual DP transmitters on a single flow element and set of taps.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 1 No |
How find CGPA? when marks are 515/850 & 2559/3350. Plz any one tell me.
in the pipe line if the control valve fails to respond to controller action,by what means we can stop the flow in the pipe line ?
what are the different types of terminal lugs used for wiring termination?
why we are maintain the gap voltage in vibration probe when installing time can explain me?
what is difference between OP AMP and differential amplifier?
Isometric drawings are generated during _________________ phase of a project
plz give me the logic for how a pushbuttoon can be worked as atoggle switch i m working with allenbradely/micrologix1200/rslogix500
what is the difference between RS 232,RS 485,RS 422, how they different from each other
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
in current transmitter why we use 4-20ma ???
Where should we terminate the shield and why?
why we set -10 volt in vibration sensor output,why not +10 volt
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)