why we use 0.2 to 1.0 kg/cm2 output in control valve
Answers were Sorted based on User's Feedback
Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
Is This Answer Correct ? | 2 Yes | 8 No |
What are the types of valves?
What is the reverse action and direct action
What is CNC
what are procedure of sox-nox calibration
hello friends, can you please send me the model paper or question paper to be prepared for hpcl examinations????????? You can mail me at rahim_here@yahoo.com waiting for your reply........... help me .. plz.....
What is the full form of PMMC ?
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
What is the difference between radar and ultrasonic level transmitter? Which method is best and more accurate?
What are the materials use for COntrol Valve body?
1 Answers KNPC, Qatar Petroleums,
i am preparing for BARC ,so plz mail me how to prepare for BARC. ALSO IF POSIBLE SOME RELATED QUESTIONS. MY MAIL ID IS khushi_4uall2003@yahoo.co.in
how to measure the output of RTD given the general formula of rtd.
How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?