why we use 0.2 to 1.0 kg/cm2 output in control valve
Answers were Sorted based on User's Feedback
Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
| Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
| Is This Answer Correct ? | 2 Yes | 8 No |
Calibration procedure for water rotameters
what is difference between positioner and position transmitter in control valve
what are the difference between conventional and smart transmitter.
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
Which standard of hazardous area classification used in India?
in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?
What are the type of bonnets in the control valves?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
what is the different between deflection type measurement and null type measurement in RTD?
What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
what is span adjusment of transmitter? what is the function of positioner/
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)