How can we calculate the resistance of earthing & how can we
control it?
Answers were Sorted based on User's Feedback
Answer / p.v.subbaiah
Earth resistance can be measured with earth megger.There is
some values for the earth resistance.For 33kv s.s the earth
values should be less than 1 ohm.etc.
To control earth
resistance with in the limited range we have to monitor the
earth pits regularly.If the values are beyond the limit
then pour salt,coal and water.Then check the values.If your
sub-station is at dry area then you have to pour some
chemical called BITUMAN COMPOUND in the earth pits.Then
your earth values are safe.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / meenakshi
i vud lyk to enhance mr.subbiah's answer...
for large power stations- 0.5 ohm
major power station - 1 ohm
small substation - 2 ohm
other cases - 8 ohm
controlling here means the measures 2 b taken to reduce the
earth resis value
- use no of earth electrodes in parrlel connection
- v can replace the existing electrode by a larger dia
electrode
- depth of pit can b icreased in order to get more moisture
n water content in the soil
-n the important method as mentioned by subbiah
Is This Answer Correct ? | 4 Yes | 0 No |
A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?
What is the function of a pressure Switch in a Substation?
what is %impedanece
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
I am a electrical engg. diploma holder,applied for junior engineer (electrical),Kolkata RRB. Have I to attend all electrical,mechanical&civil portion in written exam.???
what's the simultenous maximum demand (SMD)..what the diffrent MD and SMD?
could i arrange a faulty and healthey battery bank togather in parallel , if your ans is not then why?
what are the condition that makes hooter blow?
A 230V, 60W bulb when connected to 230v supply what current and power will consume, if same bulb is connected to 200v what purrent and power will consume?
what should be the BDV value Of 11/132kv power transformer
What is the acceptable earth resistance for Commissioning the Transformer?
Refernce currents are to be generated using refernce cueernts how can this be done