How can we calculate the resistance of earthing & how can we
control it?
Answers were Sorted based on User's Feedback
Answer / p.v.subbaiah
Earth resistance can be measured with earth megger.There is
some values for the earth resistance.For 33kv s.s the earth
values should be less than 1 ohm.etc.
To control earth
resistance with in the limited range we have to monitor the
earth pits regularly.If the values are beyond the limit
then pour salt,coal and water.Then check the values.If your
sub-station is at dry area then you have to pour some
chemical called BITUMAN COMPOUND in the earth pits.Then
your earth values are safe.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / meenakshi
i vud lyk to enhance mr.subbiah's answer...
for large power stations- 0.5 ohm
major power station - 1 ohm
small substation - 2 ohm
other cases - 8 ohm
controlling here means the measures 2 b taken to reduce the
earth resis value
- use no of earth electrodes in parrlel connection
- v can replace the existing electrode by a larger dia
electrode
- depth of pit can b icreased in order to get more moisture
n water content in the soil
-n the important method as mentioned by subbiah
| Is This Answer Correct ? | 4 Yes | 0 No |
what is meant by transformer?
what is importance of ka in mccb
What is the max demand on your transformer and your company?
10 Answers Bhel, CBRE, Core Consultants, HPL, IOCL, JLL, L&T, Lemon Tree, MNC, Rashmi, TATA, Tata Motors, Tata Power, Torrent Pharma,
Why neutral is not used in three phases dol starter
what is power and what is watts detailed description and formulas
meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
What are the disadvantages of thermal power plant?
what is the highest transmission voltage in india???
49 Answers Bhel, EIPL, Engineering, Jindal,
What is difinition of HIGH RESISTANCE FAULT and LOW RESISTANCE FAULT?
why inverter rating is in KVA
why fuse is not applicable for nutral and what will happen when it applied.
where this neutral connection goes after returning from the load(home ,factory,industries).Is it grounded at the transformer side or atthe generator side .If it is grounded then we also ground the earth connection.is there any problem with this.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)