where this neutral connection goes after returning from the
load(home ,factory,industries).Is it grounded at the
transformer side or atthe generator side .If it is grounded
then we also ground the earth connection.is there any
problem with this.
Transformer secondary side neutral is earthed.if unbalanced load condition residual return current only goes to earth it's a safest one actually.In basic ground is the very low impedance path compare to your earth rod.current always choose low resistive path.so it's not possible to return feed current flow from ground to equipment.
| Is This Answer Correct ? | 0 Yes | 0 No |
technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"
define hysteresis loss, eddy current loss and windage loss
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
What are the limitations of Kirchoff's laws?
What is the application of Dyn1 and Dyn11 vector group of transformer?
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
Name the test signals used in control system
Motor running trough VFD, if voltage reduced speed will be?
Why we have short circuit the secondary of the transformer
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
what is a circuit breaker. Weite the types of circuit breaker.
when 40 watts and 60 watts bulb is connected in series, which bulb glows brightly ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)