why transformer rating is always in KVA
Answers were Sorted based on User's Feedback
Answer / chin2
power losses depends on current (copper) and voltage (iron)
so if we take power KW it is also a factor of power factor
so we use KVA
| Is This Answer Correct ? | 32 Yes | 2 No |
Answer / tanu singh
rating of any machine is depend to the losses in that m/c.
in x-mer, the iron losses and hystersis losses dependent to
the voltage. and copper losses depend to the current. it's
the only reason to take the ratings in kva.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / saurabh bhardwaj
transformer output is always depends upon the power factor,
P=V*I*p.f, T/F has not work as a load on it when there is no
load there is no p.f. so it's rating in KVA.KVA RATING IS
GIVEN BY MANUFACTURER WHO HASN'T KNOW WHAT TYPE OF LOAD WILL
APPLY IN FUTURE BY CONSUMER.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / aditi
kVA is the unit for apparent power. Apparent power consists
of active and reactive power.
Active power is the share of the apparent power which
transmits energy from the source (generator) to the user.
Reactive power is the share of the apparent power which
represents a useless oscillation of energy from the source
to the user and back again. It occurs when on account of
some inertia in the system there is a phase shift between
voltage and current. This means that the current does not
change polarity synchronous with the voltage. But the heat
generated in a winding as well as the eddy current losses
generated in a transformer core depend on the current only
regardless of whether it aligns with the voltage or not.
Therefore the heat is always proportional to the square of
the current amplitude irrespective of the phase angle (the
shift between voltage and current). So a transformer has to
be rated (and selected) by apparent power.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / praful nandankar
As we know that copper losses depend upon square of current
and core losses depend upon voltage applied.
Apparent power is the vector sum of reactive power and
active power. active power is the useful energy transferred
from primary ckt to secondary ckt. Reactive power is used
to create magnetic flux in the core. Hence we hav to take
into account the active as well as reactive power.Hence the
rating of transformer is alwAys in KVA.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / aruna
transformer rating is mainly depends on core losses.those
losses depends on temp which can be depends on current
rating.. no need of power factor cal..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth patel
when we install any new transformer we have only load
current as known quantity accordingly the secondary voltage
is selected. but we dont know which type of load will be
connected on the secondary side it may be inductive ,
capacitive , resistive or combination of them.So as we dont
know about the load we dont know power factor of the load
thats why the ratings of transformer is in kva and not in
kw.
| Is This Answer Correct ? | 11 Yes | 13 No |
active elements are those which are capable of
what is accuracy ? in any meters , coils accuracy . how can u defined that ?
What will happen if " not connecting the neutral point to ground of diesel generator output (380 V)", also if someone touched one phase without isolation from ground during the A/M condition what will happen to him?
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)phase to phase or phase to neutral
why a fan starts rotating in the reverse direction when condenser gets damaged?
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
What is the meaning of utility ground and clean ground? How the distribution panel is grounded?
What is the HVDC Transmission System? What are the conditions applicable to lay an HVDC Line?
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
What is power factor?How to improve power factor
If genrator not build up voltage , How u can Manually Excite ?
What is Skin effect of the cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)