Answer / pramod sahoo
To protect the CT from static voltage surges resulting in
insulation falure.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sheik hussain
if secondary side open ct act as step up transformer so flux
is increased ,for that insulation is not withstand so
vibration and high voltage occurs thats why we should kept
the sec terminals closed condition..
actually ct is not have a pry turn it have only sec tunas,
pry side is like busbar cable conductor ect.,so when s1,s2
is open it mutual inductance is occurs so act as a step up
transformer.. the flux is incresed,insuation get failure
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / simon
The Eddy current's value is too high so the sec side of X-mer is grounded.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abb
Open Circuit secondary side of the Current Transformers
causes saturation due to high voltage induced.
| Is This Answer Correct ? | 0 Yes | 0 No |
Shorting is done ,when the ct is not in use or in case of
spare ct, to prevent development of high voltage in
secondary.Grounding is done to remove the influence of high
primary voltage due to capacitance between primary and
secondary, and insulation failure.
| Is This Answer Correct ? | 0 Yes | 1 No |
Differenciate between circuit wiring and sub main wiring with illustrations
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?
expalanation for 5p10 class.
What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.1)
How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?
During the troubleshooting of an inoperative shunt generator, you found the voltage to be 2+ volts; what is known from this. Is it (1). odds are the armature is good (2). odds are there is no field current flowing in field windings (3). odds are the armature is bad (4). both 1 & 2 are correct (5). both 2 & 3 are correct
Upto what extend the powerfactor of a supply system can be improved to be cost effective?
HOW TO CALCULATE EHV CABLE SIZING?
What is Biased Generator Differential Relay?
describe the Tranformer testing procedure
Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?
what is mean by xlpe swa pvc
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)