why it is necessary to short and ground of a current
transformer secondary side?
Answers were Sorted based on User's Feedback
Answer / pramod sahoo
To protect the CT from static voltage surges resulting in
insulation falure.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sheik hussain
if secondary side open ct act as step up transformer so flux
is increased ,for that insulation is not withstand so
vibration and high voltage occurs thats why we should kept
the sec terminals closed condition..
actually ct is not have a pry turn it have only sec tunas,
pry side is like busbar cable conductor ect.,so when s1,s2
is open it mutual inductance is occurs so act as a step up
transformer.. the flux is incresed,insuation get failure
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / simon
The Eddy current's value is too high so the sec side of X-mer is grounded.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abb
Open Circuit secondary side of the Current Transformers
causes saturation due to high voltage induced.
| Is This Answer Correct ? | 0 Yes | 0 No |
Shorting is done ,when the ct is not in use or in case of
spare ct, to prevent development of high voltage in
secondary.Grounding is done to remove the influence of high
primary voltage due to capacitance between primary and
secondary, and insulation failure.
| Is This Answer Correct ? | 0 Yes | 1 No |
How much voltage we need to apply in 33kv cable during hipot test of cable
do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042
the voltage per turn of a primary winding of a transformer is the same as the voltage per turn of the secondary winding of the transformer. why?
what are the colour's and their indications in bucholz relay?
how the BDV of the oil will be checked using moterised controled HV SET?
How to size Air Circuit breaker (ACB)? What is the most important factors?
why odd hormonics only will effect the power system.why not even hormonics
Name quantities which are not transformed in the tranformer.
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
What is Minimum permicible meggering value for following 1) LT Panels (Ph to Ph / Ph to Earth) 2) 11 KV, HT Panels (Ph to Ph / Ph to Earth) 3) 11 KV Cable 4) LT Cable
What is distance protection relay? where & why we use this relay?
2 Answers Siemens, UltraTech, Voltech,
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)