Check the resistance of the three winding it should be balance.
Then check for any grounding all the winding should show
resistance in mega ohm.
rotate the rotor it should freely rotate this will confirm
no bearing damage.
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / will bg
Prove your meter/megger on a known resistance block. You
should remove any star or delta connection/bridges if at all
possible. If your earth/ground reference is not the motor
frame itself (i.e. a conductor in a cable) then first prove
your earth/ground by measuring on ohms the resistance
between your earth test point to various places on the motor
frame. You should get almost 0 ohms. Now measure your
phase resistances and they should always be fairly equal.
Rule of thumb is 10% variance. Remember the bigger the
motor the lower the resistance. Now on 500 volts DC measure
all phases to earth. Now switch megger to 1000V DC and
measure phase to phase resistance.
| Is This Answer Correct ? | 6 Yes | 7 No |
Explain types soft starters?
What do you mean by turns ratio of instrument transformer?
what is the difference between electrical and electronic choke?
we want to feed 3 phase supply to 70 ton AC load.what will be the size of (3 phase)cable require.
can anyone help me regarding bout Electrical designs and calculations .. which text book should i follow as i am a trainee engineer.Description of my work which is Electrical designs like cable sizing, lighting, lightning, Gensets sizing, motor sizing, transformer sizing, generator sizing, circuit breakers, PDB MCC PCC SLDB MLDB panels, Single line diagrams mainly, substation desings, cable routing and layouts, reactive power compensations, power factor improvement, voltage drop calculations, power generations, power transmission, power distributions all calculations.Please help me
What is formula calculation size cable wire ?
what is the capital of india
13 Answers eInfochips, Reliance,
why single phase to grd test in HV cable?why not 2 phase at a time?
If oil and air can withstand a high MeV when used as an insulator in a transformer, what are the values of how high for each material?
in cable joints procedure what electrical problems have been solved out ?
How can get elongation of 2 k.G aluminium, if elongated aluminium dia is 2.5 mm?
In a 11000/440 V transformer, when any one phase of 11 KV supply fails (ie., single phasing), what happens to the secondary voltage and why?
3 Answers Secure Meters, TCS, Torrent Power,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)