How can we parallel two transformer with vector gorup YNd11
and YNd1?How is connection two transformer GT?
Answers were Sorted based on User's Feedback
It is advised not to parallel the two transformers because
of the difference in their phase shifts. For YNd11 the HV
lags the LV by 30 degrees while in YNd1 the HV leads the LV
by 30 degrees. Parallelling the two will lead to over
heating and other abnormal conditions which may lead their
protective relays to malfunction.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / k.prakashchandra
If phase sequence of YNd11 is RYB,then of YNd1, it may be YBR
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / nasssem
it can be paralleled by reversing the phase sequence of one
of them. For example, a transformer with Yd11 connection
can be paralleled with that having Dy1 connec-tion by
reversing the phase sequence of both primary and secondary
terminals of the Dy1 transformer.
| Is This Answer Correct ? | 2 Yes | 3 No |
what is the meaning of servo motor. In trains, what type of the motors we are using at the bottom of each compartment
Please let me know DG set b check how many hour and days.
Car battery + terminal allways biger than - terminal! Why?
how will be power factor while using the resistive load and Capacitive load?
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.
Why 66KV is step down to 11KV and then 433v, not directly 66KV to 433v ?
how to choose cable size with respect to load? how to convert cable size in mm2 to sq.mm?
Did RMU have ct and pt ?
sir i am ece engineer.i want to job in power plant.what is the best option for me as electrical engineer or instrumentation engineer?pls reply me.
1.Why use in ups in software's,reason,and pls explain. 2.what is the isolation transformer and main use it's functioning and partes.
why frequency meter is connected in parallel in a circuit?
1 Answers University of Engineering and Technology,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)