How can we parallel two transformer with vector gorup YNd11
and YNd1?How is connection two transformer GT?
Answers were Sorted based on User's Feedback
It is advised not to parallel the two transformers because
of the difference in their phase shifts. For YNd11 the HV
lags the LV by 30 degrees while in YNd1 the HV leads the LV
by 30 degrees. Parallelling the two will lead to over
heating and other abnormal conditions which may lead their
protective relays to malfunction.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / k.prakashchandra
If phase sequence of YNd11 is RYB,then of YNd1, it may be YBR
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / nasssem
it can be paralleled by reversing the phase sequence of one
of them. For example, a transformer with Yd11 connection
can be paralleled with that having Dy1 connec-tion by
reversing the phase sequence of both primary and secondary
terminals of the Dy1 transformer.
Is This Answer Correct ? | 2 Yes | 3 No |
how we provide neutral earth on synchronising panel as per electrical standards?
what is difference between 2 pole structure and 4 pole structure in transformer yard
what is subtransient , transient and steady stateac components
Can anyone tell me what will happen if AC & DC supply get mixed???
what is the method of earthing of a transformer using electrodes?
Any Electrical Engineering jobs?Please refer for interviews. Thank you
Thermal withstand capability under full short circuit conditions, in terms of number of times of occurrence of short circuit and corresponding anticipated percentage reduction in transformer life.
any one can explain the stages of a knee point which is taken during ct magnetising curve.
Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?
What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?
why ac current do not save
in single phase we get 220 volt and in three phase 4420 v why this second Ques= in case three phase star conection our neutrul becom disconect what happan 3 Q=== a three phase house load and have unbalce load on different pahse diffrent current eg phase a 7A b 8A c 5A and voltage is 440 than how calculate it total load in kw pl give formula thanks