We have 2 Nos. Transformer with the capacity of 2000KVA and
1250 KVA and currently using only one 2000KVA T/R during
operational hours while non- operational hous 1250 KVA T/R
also used to reduce T & D losses. Similarly, 2 capacitor
bank of 500KVAR and 300 KVAR also installed to balance
reactive power. Now problem is around 1000 KW load PF is
not maintaning 0.99 as 350 KVAR capacitor is in healty
condtion. Now the PF is maintain 0.95 to 0.96.
Answers were Sorted based on User's Feedback
Answer / arvind
You please check out the location of the capacitor banks
means whether it is away from the load or not if it is away
from tha load then power losses will be there and affects
the power factor.
secondly, if the load (1000kw) is variable means motor,
then it is difficult to get power factor 0.99.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / muhammad azeem butt
we know that transformer is a inductive device it also
effect on our pwer factor lagging.
Power and distribution transformers, which work on the
principle of electron-magnetic
induction, consume reactive power for their own needs even
when its secondary is not
connected to any load. The power factor will be very low
under such a situation.
To improve the power factor it is required to connect a
fixed capacitor or a capacitor
Sl.no kVA rating of the transformer kVAr required for
compensation
1 upto and including 315 kVA 5% of kVA rating
2 315 kVA - 1000 kVA 6% of kVA rating
3 Above 1000 kVA 8% of kVA rating
Is This Answer Correct ? | 1 Yes | 0 No |
What is the difference between 11kv/110v & 33kv/110v ? If both 11 & 33KV give 110v then what is the diiference ?
on what factor insulation resistance depends
HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?
how many typetesting of transformers?
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
what happen if ac supply is fed to rotor of the alternator
What is the maximum load an electric engine can pull??
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
how we can find out the speed of fan without using any measuring instrument
Dear Mr B C pal...Can you plz. put some light on principle of operation of Z-Ct in conjunction to its use with 1Cx1000Sqmm HT Cables & Directional Ground Fault / Over Voltage Relays...Regd..Parag v K 9899115632
What is resolution of a measurement?
How should i design a 1ph & 3 ph transformer. Kindly let meknow all steps and formulaes related to design from scratch.