Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We have 2 Nos. Transformer with the capacity of 2000KVA and
1250 KVA and currently using only one 2000KVA T/R during
operational hours while non- operational hous 1250 KVA T/R
also used to reduce T & D losses. Similarly, 2 capacitor
bank of 500KVAR and 300 KVAR also installed to balance
reactive power. Now problem is around 1000 KW load PF is
not maintaning 0.99 as 350 KVAR capacitor is in healty
condtion. Now the PF is maintain 0.95 to 0.96.

Answers were Sorted based on User's Feedback



We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one ..

Answer / arvind

You please check out the location of the capacitor banks
means whether it is away from the load or not if it is away
from tha load then power losses will be there and affects
the power factor.
secondly, if the load (1000kw) is variable means motor,
then it is difficult to get power factor 0.99.

Is This Answer Correct ?    4 Yes 0 No

We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one ..

Answer / muhammad azeem butt

we know that transformer is a inductive device it also
effect on our pwer factor lagging.
Power and distribution transformers, which work on the
principle of electron-magnetic
induction, consume reactive power for their own needs even
when its secondary is not
connected to any load. The power factor will be very low
under such a situation.
To improve the power factor it is required to connect a
fixed capacitor or a capacitor

Sl.no kVA rating of the transformer kVAr required for
compensation
1 upto and including 315 kVA 5% of kVA rating
2 315 kVA - 1000 kVA 6% of kVA rating
3 Above 1000 kVA 8% of kVA rating

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

testing of transformer

1 Answers   Vijai Electricals,


Dry type transformers

0 Answers  


1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?

0 Answers  


How is the Depth of Stator Slot being calculated for Synchronous Generator?

2 Answers  


What is the size of electrical cable to be used for a space heater single phase 240V ?

3 Answers  


what is bus pt and what is the function of it ???

8 Answers   TATA,


Does the Impedance of the source affects the THD

1 Answers  


why in a transformer frequency remains constant? if frequency is changing what will happen?

5 Answers  


What is the formula to find maximum load of a DG (Single phase and Three phase)?

1 Answers  


can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?

0 Answers   UPSC,


what is the relationship between phase & neutral

0 Answers  


why motor burns ?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)