Answer / sebastian
ESD valve or EIV(Emergency Isolation valves) are only used
(operates)for Emergency conditions only, usually theses
valves are reamins open till incase any Emergency occures
that is fire .some times it remains open till plant next
turnaround@3-4 years).so valve trim or actuator may stuck
due to some reason and valve never clos when real
Emergency, to avoid this situation , goverment athority or
insurance company guidlines are given to plant operation
section to check availablity and functionality of ESD
valves periodically, may be each 3 month, 6 month etc.
Partial stroke: Valve start to move from its open position
to close postion only @20-25% of its total traval(to avoid
process upest)and return back.there is a Function logic
built in the ESD logic with Protection timer(incase valve
limit switch not moved from open postion at set time the
logic will re set for valve its open condition and
indicate failed.(partial stroke test failed) .
if valve moved from open position (by means of limt switch
leves its contact)logic will re set and remais for open
position and indicate succes test.
if any details requred with logic contact me
sebalukose@gmail.com
| Is This Answer Correct ? | 8 Yes | 0 No |
ESD's are checked anually by applying partial signal from
DCS to ESD's.They are made to open partial and checked.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / robert
Esd valves are required by gov. safety standards to be
checked periodically to be able to stroke i.e. (move to a
determined position, usually 90 % and back to original
position.) If the valve does as required, it passes
function test and can remain in service. In some
applications valves tend to stay in one position for long
periods of time. This often has an effect on the
bearings "freezing" up, and in an emergency situation the
valve may not close when required.
| Is This Answer Correct ? | 2 Yes | 1 No |
Q- Control problem are mainly classified in _____ types. a-)4 b-)3 c-)6 d-)nono of these Few of them i know is 1- regulator type problem (eg- Air conditioner) 2- tracking problem (eg missile trcking problem) 3- sybernatics 4- optimal control problem
What is cv of control valve
What inherent design and operating principles are included in a modern control system to use predictive maintenance practices to increase overall system reliability?
Is Hart communicator calibration device or communicating device for transmitter?
what is rtd
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
What is controller? What is transmitter?
In Safe Guarding test what means by "Failed to Danger" ?
What is the difference between PLC-HMI and DCS as each function of DCS based system is possible in PLC ?
without a positionar can a control valve operate? give the difference of operating with positionar and without positionar?
how to design orifice plate?what is the equation?
what is the differnt between open loop and close loop ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)