How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?
A Thermal Instrument was flow calibrated at the factory for a certain specified medium/fluid. If their flow meters can be recalibrated in the field for fluids other than the one specified at time of manufacture, the calibration instructions are not posted on the web site.
Their web site does have a fairly long and involved calibration check for landfill gas application (methane generated in garbage dumps/landfills) under the FAQ: What is your procedure on checking the calibration of a landfill gas meter in the field? It involves on-site multiple pitot flow measurements in a traversing pattern to get a flow average, calculating m molecular weight of the gas mixture, calculating density from the ideal gas law, and then converting to velocity and finally calculating mass flow with the tube's cross sectional area. Simple, huh?
The analog output of the transmitter, the zero at 4.00mA and the span at 20.00mA, can be adjusted with a field calibration check and adjusted as necessary.
Typically, the flow rate can only be calibrated on a certified flow stand or flow cell; field calibration is not practical. Return to the factory is typical.
Carl Ellis Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
What is NODE in DCS?
In most process, speed of motor controlled by control system with a reference pot . Now if i start & it becomes uncontrollable, i.e.gets directly start & stop after certain time.Then which reasons can make such problem? can motor may be faulty?how?
WHAT DO YOU MEAN BY LOOP IN C.
when i installed Allen_bradley_RsLogix_500_Pro_V_7.0,after installation it gives the fatal error.it need activation file.from where and how i can find its activation file.
WHAT IS TMXT IN TEMPERATURE FOUNDATION FIELDBUS.
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
what is meant by control valve sizing?
can u plz send me technical questions asked in SCHNEIDER ELECTRICAL technical paper?
Why is it necessary to use compensation leg to measure the liquid level in a closed or pressurized tank?
1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?
3 Answers EI Electrotechnical Institute,
What is difference between sensors and transducers?