pressure switch range 0 to 2bar.i have to install from
ground level to 5 meters height.what is the formula the to
increse the range ? and every 1 meter how much pressure
should be add ?
Answers were Sorted based on User's Feedback
Answer / rajkumar.diice
At first you
should know
clearly the
correct fluid
density. If you
are working with
water; the water
density is
1000kg/m3.
Multiply this
with the tank
height 5 meters
then the
pressure acting
on switch at
liquid level 5
mts will be
5000mmWC, set
switch setting
at .5 bars. If
you are looking
to switch a
motor off
automatically
means use NC
contact.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / mrmk
It depends upon the tapping point.In your case if the
tapping point is at ground level and pressure switch
installed above ground level then no need of any
compensation.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mohsin malek
my ans is pressure is depend upon matrial density
supose water density is 1000kg/m3 multiply by tank hight
| Is This Answer Correct ? | 0 Yes | 0 No |
how is work pressure switch& level switch?what is the principle of this?
What is the function of solenoid valve in on/off & shutdown valve and why it is not used in control valve normally?
What is the differerence between hysterisis and linearity.
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
why pneumatic control signal output is use 0.2 to 1 kg/cm2
what is the principle of ultrasonic flowmwter and radar type flowmeter?
Lube oil pressure transmitter local it's showing 9.8 kg/cm2 but dcs side it's showing 9.26 like that what is the reason?
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
HOW CREATED LP & HP PRESURES IN DRUM FOR DRUM LEVEL MEASUREMENT!
IF PLC POWER FAILURE THEN WHAT HAPPEN?
What is duty of as-built engineer.
thermocouple output is AC OR DC??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)