Often identification data is printed on proximity (or prox) sensor's label but it is not uncommon for the label to damaged, missing or unreadable.

Many prox sensors are DC powered, 3 wire devices that conform to a standard wiring color code:

brown is (+) supply voltage, typically 24Vdc
blue is (-) supply voltage common or return
black is the sensor's switched output

To test a 3 wire sensor to determine whether it is a PNP or NPN type you need a DC power supply and a DC voltmeter.

Set the meter to DC voltage to a range greater than the supply voltage (typically 24Vdc), like 50/100/200/600V

The black meter probe should be in the 'common' meter socket
The red meter probe should be in the DC 'volts' socket

Connect the sensor's brown wire to the power supply (+)
Connect the sensor's blue wire to the power supply (-).

Turn the power supply on.

Ensure that the prox sensor is not triggered by presence to an object.

Connect the black meter probe to the blue sensor wire.
Connect the red meter probe to the black switched signal output sensor wire.

If the meter is connected to a PNP device, the meter will read 0V.
If the meter is connected to an NPN device, the meter will read 24Vdc.

Force the sensor to change state/output by detecting an object.
- If it is an inductive proximity switch, place a piece of metal in front of the sensor.
- If it is a photoelectric sensor, block the photoelectric beam.
- For an ultrasonic sensor or a capacitive sensor, you can just use your hand to make the sensor output. Some prox sensors use an LED that lights up when the sensor detects an object.

With an object present, a PNP device's output will change and the voltmeter readout will read 10V to 30V. This is also known as a "sourcing" device.

With an object present, an NPN device's output will change and the voltmeter readout will be 0V. This is also known as "sinking."

Another test to check for PNP:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.

When sensing no object, the signal output will be 10V to 30V.

When sensing an object, the signal output will be 0V.

Another test to check for NPN:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.

When sensing no object, the signal output will be 0V.

When sensing an object, the signal output will be 10V to 30V.

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.

1 Answers  


Instrumentation engineer please reply me,I am electrical engineer ,what is the future in instrumentation dept {presently working (P&ID) Design} for me,whether good future for me as instrumentation department.what side can i get job in future

3 Answers  


Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?

0 Answers  


IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK

1 Answers  


What are different types of control valves?

0 Answers  






in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?

2 Answers  


In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.

4 Answers  


A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.

0 Answers   MNC,


If we increase only P what will be controller action ?

0 Answers   IMECO,


On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of the tank while low side port connected to the top. I would like to know how to fill the glycerin on its low side with two condensing pot installed,one from top and the other one for its drain line.Please I need your expertise...thanks

1 Answers  


what is temperature compensation?

1 Answers  


how to measure the output of RTD given the general formula of  rtd.  

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)