pressure switch range 0 to 2bar.i have to install from
ground level to 5 meters height.what is the formula the to
increse the range ? and every 1 meter how much pressure
should be add ?
Answer Posted / rajkumar.diice
At first you
should know
clearly the
correct fluid
density. If you
are working with
water; the water
density is
1000kg/m3.
Multiply this
with the tank
height 5 meters
then the
pressure acting
on switch at
liquid level 5
mts will be
5000mmWC, set
switch setting
at .5 bars. If
you are looking
to switch a
motor off
automatically
means use NC
contact.
| Is This Answer Correct ? | 11 Yes | 1 No |
Post New Answer View All Answers
Explain the burnout feature.
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
Explain the working of an enraf level gauge.
which processor is used in dcs.
need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate
pls suggest suitable MOC of diaphragm for pressure measurement of UREA grade solution service fluid.
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
Explain the difference between plc and cnc?
What is motion balance principle?
what is dc moter.
Questions on flow meters,few questions on HART protocol,
tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),
draw shematic diagram of c/v positioner(smart type)?
Why humidity limit is 30 to 55 % for raw material storage?