how pressure reduce through pressure control valve? suppose
we have to reduce 20 kg pressure to 10 kg pressure , then
what we do ? open the valve or close the valve , initially
it is 20 % is upon ( for ur knowledge ).
Answers were Sorted based on User's Feedback
My dear,
In control valve we ll compare the setpoint(operator interference value) and the actual pressure on the line.this deviation is given to the control valve.When the error is positive(means pressure is high),the C/V starts closing and when the error is negative(means pressure is low),the C/V opens and maintains the pressure.
One more thing,why u need to fix the low limit of control valve to open 20%.Depending on the deviation the controller controls the process pressure.
Finally,the controller tuning is must for this control.play with the gain and integral time and deadband to make steady process..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / daxish_02
If pipe size is same before and after so this answer is correct..
basic fundamental behind the general formula that is
pressure=force/area......ok
here pipe size is fixed...ok
assume 20% valve open....than area of pipe cover after the valve is more so we get some pressure..
assume that valve open 40% so area of material flowing through valve increase so pressure decrease after the valve.....
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / g.s.arun
to open the byepass valve ,to reduce the pressure 20kg to 10 kg.
| Is This Answer Correct ? | 1 Yes | 4 No |
What is differnece between leveltroll and interface leveltrol?
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
What materials are used in thermo wells?
what is bms?
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?
How to calculate 47Liter H2 Gas cyilnder consumtion? Cylinder inlet Pressure is 200bar and Discharge pressure is 6.0bar. Flow is 100ml/min.For the above condition how many days one cylinder can be used?
How to calibrate the control valve.
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
what is ment by PID controllers? explain with example?
Consider a control valve action,the inlet air pressure is only 6 ksc but physically how it can be operate against 100 ksc line fluid pressure?
Can anybody explain about wellhead control system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)