how pressure reduce through pressure control valve? suppose
we have to reduce 20 kg pressure to 10 kg pressure , then
what we do ? open the valve or close the valve , initially
it is 20 % is upon ( for ur knowledge ).
Answers were Sorted based on User's Feedback
My dear,
In control valve we ll compare the setpoint(operator interference value) and the actual pressure on the line.this deviation is given to the control valve.When the error is positive(means pressure is high),the C/V starts closing and when the error is negative(means pressure is low),the C/V opens and maintains the pressure.
One more thing,why u need to fix the low limit of control valve to open 20%.Depending on the deviation the controller controls the process pressure.
Finally,the controller tuning is must for this control.play with the gain and integral time and deadband to make steady process..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / daxish_02
If pipe size is same before and after so this answer is correct..
basic fundamental behind the general formula that is
pressure=force/area......ok
here pipe size is fixed...ok
assume 20% valve open....than area of pipe cover after the valve is more so we get some pressure..
assume that valve open 40% so area of material flowing through valve increase so pressure decrease after the valve.....
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / g.s.arun
to open the byepass valve ,to reduce the pressure 20kg to 10 kg.
| Is This Answer Correct ? | 1 Yes | 4 No |
WHAT IS ANNUBAR?
what is mean by hot loop and cold loop testing, whts different between both
Can anyone help me with the Question bank(objective type) for complete Instrumentation engineering,either a soft copy or a Hard copy(Book),or the name of the author ,or publisher.
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
what is the conductivity sensor output formula and what is the ph sensor output formula?
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
What is hook's law
Explain the working of an enraf level gauge.
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
Can 2 transmitters be connected to Integral orifice meter taps? Does an integral orifice comes with 2 set of taps?
What safety precautions you will adopt to work on Steam service control valve?
Tell me about the synchronization panel.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)