Answer / eswar
we are using 4 ma instead of 0 ma because the in order to
differentiate 0 input and fault condition(open circuit cable
or transmitter).
we are using maximum of 20ma because current above range can
cause fire or spark from short circuit conditions due to
weak installations.
| Is This Answer Correct ? | 56 Yes | 8 No |
Answer / abdus sattar mollah
initially,0-20ma of current is used as an transmitting
standard unless a objection was met.It was that:0 ma of
current used to indicate no signal/minimum signal from a
signal conditioner but if there is a faulty condition(such
as loop break),then also it will be show 0 ma of
current.Operator may think that there is no signal but
actually a fault has occured.So he cant distinguish between
them unless the plant is damaged.This is called TRUE ZERO.
So,after a reserach a new standard was proposed i.e 4-20 ma
of current.There was minimum interference in this
range,good quality transmittance,low power consumptions.So
this satndard is used.
| Is This Answer Correct ? | 37 Yes | 1 No |
Answer / deepesh
1) As stated earlier, 4mA is used to avoid the conflict
between live zero and dead zero.
2)In 4 mA to 20 mA range, current to pressure converter
gives linear output.
3)This range is intrinsically safe.
4)Low power consumptions
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / v.r.m.kiran
We are using 4 to 20ma because
1. Distinguish between process Zero & Instrument Zero.
2. It is easy to convert 4 to 20ma to 1 to 5v(Digital
Signal) by using a 250 Ohms Resistor in series.
V = IR
V=4*250=1000 MV = 1V, 8*250=2000 MV = 2V, 12*250=3000 MV =
3V, 16*250=4000 MV = 4V, 20*250=5000 MV = 5V.
3. Now we are using digital Indicators for display. Olden
days there will be analog display meter in the transmitter
for indication(0 to 100)%. When we apply 4ma or while
checking the transmitter online pointer should indicate
zero then we say that instrument is working correctly but
it comes bellow zero we have to check our instrument & have
to calibrate.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / nagarajan audaiyarpatti
In the fault or open condition we cannot find the 0mA as 0
sothat the 4 mA consider as a zero and 20mA as a span ,in
this condition we can maintain 250mohms in the loop,sothat
we use usually 4 to 20 mA instead of 0 to 20mA in the
transmitter for measuring all the parameter such as
pressure ,temperature ,level,flow.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sachin bijole
there is no required above current of 4 mA at zero % range b'cause of faulty condition we think the current have found 0 signal.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hari
In industry we using 4 to 20 MA b'cuz drop of voltage will
less ...the signal will transmit long distance ..so sme
kind of drop voltage will there ..
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / mr gauge
We use 4mA instead of zero because 4mA is a minimum current
required to power up the transmitter, positioner etc. How do
we get the device turn on with no current.
| Is This Answer Correct ? | 7 Yes | 34 No |
why we are using ungrounded RTD sensor and what is difference between grounded RTD and Ungrounded?
HOW MANY METHODS OF TEMPERATURE MEASUREMENT ? HOW MANY MEASURING DEVICES / TRANSDUCERS ?
6 Answers Aramco, IOCL, JP Group, NFCL,
what master plc do?
why we use 24v dc in instrument rahter than 230vac????
What is the relationship between Sensor
Explain Split Range Control In Control Valve Briefly.
what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better
how to use K thermocouple instead E- type without compesation cable
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
describe yourself?
What is the expansion of RADAR? How it works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)