Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why are use only 4 to 20ma. signal.

Answers were Sorted based on User's Feedback



why are use only 4 to 20ma. signal...

Answer / eswar

we are using 4 ma instead of 0 ma because the in order to
differentiate 0 input and fault condition(open circuit cable
or transmitter).
we are using maximum of 20ma because current above range can
cause fire or spark from short circuit conditions due to
weak installations.

Is This Answer Correct ?    56 Yes 8 No

why are use only 4 to 20ma. signal...

Answer / abdus sattar mollah

initially,0-20ma of current is used as an transmitting
standard unless a objection was met.It was that:0 ma of
current used to indicate no signal/minimum signal from a
signal conditioner but if there is a faulty condition(such
as loop break),then also it will be show 0 ma of
current.Operator may think that there is no signal but
actually a fault has occured.So he cant distinguish between
them unless the plant is damaged.This is called TRUE ZERO.

So,after a reserach a new standard was proposed i.e 4-20 ma
of current.There was minimum interference in this
range,good quality transmittance,low power consumptions.So
this satndard is used.

Is This Answer Correct ?    37 Yes 1 No

why are use only 4 to 20ma. signal...

Answer / deepesh

1) As stated earlier, 4mA is used to avoid the conflict
between live zero and dead zero.

2)In 4 mA to 20 mA range, current to pressure converter
gives linear output.

3)This range is intrinsically safe.

4)Low power consumptions

Is This Answer Correct ?    17 Yes 2 No

why are use only 4 to 20ma. signal...

Answer / v.r.m.kiran

We are using 4 to 20ma because
1. Distinguish between process Zero & Instrument Zero.
2. It is easy to convert 4 to 20ma to 1 to 5v(Digital
Signal) by using a 250 Ohms Resistor in series.
V = IR
V=4*250=1000 MV = 1V, 8*250=2000 MV = 2V, 12*250=3000 MV =
3V, 16*250=4000 MV = 4V, 20*250=5000 MV = 5V.
3. Now we are using digital Indicators for display. Olden
days there will be analog display meter in the transmitter
for indication(0 to 100)%. When we apply 4ma or while
checking the transmitter online pointer should indicate
zero then we say that instrument is working correctly but
it comes bellow zero we have to check our instrument & have
to calibrate.

Is This Answer Correct ?    10 Yes 3 No

why are use only 4 to 20ma. signal...

Answer / nagarajan audaiyarpatti

In the fault or open condition we cannot find the 0mA as 0
sothat the 4 mA consider as a zero and 20mA as a span ,in
this condition we can maintain 250mohms in the loop,sothat
we use usually 4 to 20 mA instead of 0 to 20mA in the
transmitter for measuring all the parameter such as
pressure ,temperature ,level,flow.

Is This Answer Correct ?    3 Yes 1 No

why are use only 4 to 20ma. signal...

Answer / sachin bijole

there is no required above current of 4 mA at zero % range b'cause of faulty condition we think the current have found 0 signal.

Is This Answer Correct ?    0 Yes 0 No

why are use only 4 to 20ma. signal...

Answer / rahul

why only 4-20 mA why not 8 to 30ma

Is This Answer Correct ?    4 Yes 5 No

why are use only 4 to 20ma. signal...

Answer / hari

In industry we using 4 to 20 MA b'cuz drop of voltage will
less ...the signal will transmit long distance ..so sme
kind of drop voltage will there ..

Is This Answer Correct ?    2 Yes 4 No

why are use only 4 to 20ma. signal...

Answer / mr gauge

We use 4mA instead of zero because 4mA is a minimum current
required to power up the transmitter, positioner etc. How do
we get the device turn on with no current.

Is This Answer Correct ?    7 Yes 34 No

Post New Answer

More Instrumentation Interview Questions

why we are using ungrounded RTD sensor and what is difference between grounded RTD and Ungrounded?

1 Answers  


HOW MANY METHODS OF TEMPERATURE MEASUREMENT ? HOW MANY MEASURING DEVICES / TRANSDUCERS ?

6 Answers   Aramco, IOCL, JP Group, NFCL,


what master plc do?

2 Answers   ISRO, Yokogawa,


why we use 24v dc in instrument rahter than 230vac????

4 Answers  


What is the relationship between Sensor

6 Answers  


Explain Split Range Control In Control Valve Briefly.

5 Answers  


what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better

1 Answers  


how to use K thermocouple instead E- type without compesation cable

1 Answers  


How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer

0 Answers  


WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??

2 Answers   IOCL,


describe yourself?

1 Answers   TCS,


What is the expansion of RADAR? How it works?

7 Answers   RasGas,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)