suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?

Answers were Sorted based on User's Feedback



suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the T..

Answer / kashif

Isolate the Tx from process and fully depressurized it and checked if it reads 4 Ma then calibration is OK and carried out flushing of both impulse lines and gain take it in service it should read zero or 4 Ma.

Is This Answer Correct ?    2 Yes 0 No

suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the T..

Answer / bala

if the transmitter shows 4.5ma at zero pressure. we need to trim the tx by using hart communicator. there is an option in hart digital to analog trim. go to that option and make a trim and so if not D/A trim not proper then last need to replace the new transmitter.

Is This Answer Correct ?    2 Yes 0 No

suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the T..

Answer / rajesh

After the transmitter calibration they already fix the
transmitter on the prosces line. that time u check the
process line how mach pressure and check the 5 way manifold
condition and check the LP side impulseline chook. if its
ok manifold and impules line; open 5 way manifold equlizer
valve close any one hp or lp isolation valve that time tx
should be show zero 4ma. not showing 4ma. trim it zero.
zero not trimed cheange the transmitter.
Importent.
check the LRV how much its Zero Or not.
and check the wich type of transmitter.
if it is level transimtter that one different type of
callibration. check the where using the prossce line.
thank you
rajesh

Is This Answer Correct ?    0 Yes 0 No

suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the T..

Answer / balakrishnan

no. it wont affect the pocess.

Is This Answer Correct ?    0 Yes 8 No

Post New Answer



More Instrumentation Interview Questions

Witch type cable use for rtd ,why?

2 Answers   Sugar Factory,


What is the use of valve positioner?

1 Answers   CCIE,


Why do we need to install hook-up line differential pressure type level transmitter when the differential pressure type level transmitter with capillary are available?

2 Answers  


For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5

0 Answers   L&T, Shiv Tech Marine Control,


Convert a pressure, level, flow, or temperature process variable value into the appropriate pneumatic or electrical value given different types of instruments.

6 Answers   Jindal, MCL, Thermax,






I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.

1 Answers  


can you send remote seal interface level transmitter calculation steps for oil water saperator.

0 Answers   Thermax, Sasol Firm,


What is the use of double seated valve?

0 Answers  


How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?

2 Answers  


how is work pressure switch& level switch?what is the principle of this?

0 Answers   Binani,


What is the Temperature Co-officient of Resistance of PT- 1000 and PT-2000 ?

2 Answers   Adani, Birla, MEIL,


give me the formula for analog to digital converter and also d to a converter

0 Answers   ACC,






Categories
  • Civil Engineering Interview Questions Civil Engineering (5070)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4442)
  • Electrical Engineering Interview Questions Electrical Engineering (16578)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1091)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2986)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (122)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1376)