suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
Answers were Sorted based on User's Feedback
Answer / kashif
Isolate the Tx from process and fully depressurized it and checked if it reads 4 Ma then calibration is OK and carried out flushing of both impulse lines and gain take it in service it should read zero or 4 Ma.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bala
if the transmitter shows 4.5ma at zero pressure. we need to trim the tx by using hart communicator. there is an option in hart digital to analog trim. go to that option and make a trim and so if not D/A trim not proper then last need to replace the new transmitter.
| Is This Answer Correct ? | 2 Yes | 0 No |
After the transmitter calibration they already fix the
transmitter on the prosces line. that time u check the
process line how mach pressure and check the 5 way manifold
condition and check the LP side impulseline chook. if its
ok manifold and impules line; open 5 way manifold equlizer
valve close any one hp or lp isolation valve that time tx
should be show zero 4ma. not showing 4ma. trim it zero.
zero not trimed cheange the transmitter.
Importent.
check the LRV how much its Zero Or not.
and check the wich type of transmitter.
if it is level transimtter that one different type of
callibration. check the where using the prossce line.
thank you
rajesh
| Is This Answer Correct ? | 0 Yes | 0 No |
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Draw block digram for well head from well to shipping pump?
How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?
How to check range of DP Transmitter
WHAT IS ANNUBAR?
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
why is an oxygen sensor used in a boiler stack
relation between flow and differential pressure.
Definition of reverse and acting controllers:
Briefly describe instrumentation job
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
wich is coming the first HAZOP OR SIL
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)