suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
Answers were Sorted based on User's Feedback
Answer / kashif
Isolate the Tx from process and fully depressurized it and checked if it reads 4 Ma then calibration is OK and carried out flushing of both impulse lines and gain take it in service it should read zero or 4 Ma.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bala
if the transmitter shows 4.5ma at zero pressure. we need to trim the tx by using hart communicator. there is an option in hart digital to analog trim. go to that option and make a trim and so if not D/A trim not proper then last need to replace the new transmitter.
| Is This Answer Correct ? | 2 Yes | 0 No |
After the transmitter calibration they already fix the
transmitter on the prosces line. that time u check the
process line how mach pressure and check the 5 way manifold
condition and check the LP side impulseline chook. if its
ok manifold and impules line; open 5 way manifold equlizer
valve close any one hp or lp isolation valve that time tx
should be show zero 4ma. not showing 4ma. trim it zero.
zero not trimed cheange the transmitter.
Importent.
check the LRV how much its Zero Or not.
and check the wich type of transmitter.
if it is level transimtter that one different type of
callibration. check the where using the prossce line.
thank you
rajesh
| Is This Answer Correct ? | 0 Yes | 0 No |
can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know
Can anybody tell me application of PLC,DCS,SCADA.
The wire is disconnected from the temperature sending unit (magnetic gauge). A voltmeter connected to the wire reads 0v. What does this indicate?
radial & axial vibration sensor output voltage is ac or dc volt?
Difference between 2-Valve Manifolds, 3-Valve Manifolds and 5-Valve Manifolds 3 with diagram
give some question relative instrument fitter?
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
please tell me how maintainence person shifted to good epc company/design company
list of flame proof certification ?
d/p flow transmitter LP side give to pressure.what you geting out put ? how you get(ma)?
CAN YOU USE MOVING COIL METER FOR MEASURING A.C?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)