suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
Answers were Sorted based on User's Feedback
Answer / kashif
Isolate the Tx from process and fully depressurized it and checked if it reads 4 Ma then calibration is OK and carried out flushing of both impulse lines and gain take it in service it should read zero or 4 Ma.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bala
if the transmitter shows 4.5ma at zero pressure. we need to trim the tx by using hart communicator. there is an option in hart digital to analog trim. go to that option and make a trim and so if not D/A trim not proper then last need to replace the new transmitter.
| Is This Answer Correct ? | 2 Yes | 0 No |
After the transmitter calibration they already fix the
transmitter on the prosces line. that time u check the
process line how mach pressure and check the 5 way manifold
condition and check the LP side impulseline chook. if its
ok manifold and impules line; open 5 way manifold equlizer
valve close any one hp or lp isolation valve that time tx
should be show zero 4ma. not showing 4ma. trim it zero.
zero not trimed cheange the transmitter.
Importent.
check the LRV how much its Zero Or not.
and check the wich type of transmitter.
if it is level transimtter that one different type of
callibration. check the where using the prossce line.
thank you
rajesh
| Is This Answer Correct ? | 0 Yes | 0 No |
what is diffrance between FF & SMART, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
which type of rtd is good for any system,2wire,3wire or 4 wire
What is passive connection of instrument in different types of IO module?
why the SCAN time of DCS is more & that of PLC is less? if the SCAN time of DCS then why we use DCS.
Questions on flow meters,few questions on HART protocol,
i want to control the temp of sand(welding flux) between the range of 150deg C to 170deg C. sugges me sum temp control method without PID controller.
What is the differace between Volumatric flow meter and Mass flow meter.
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
what is the calibration procedure for transweigh make weigh feeder?
why we are using perforted cable tray for control cable and ladder tray for power cable
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
What is the start up procedure of desalter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)