suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
Answers were Sorted based on User's Feedback
Answer / kashif
Isolate the Tx from process and fully depressurized it and checked if it reads 4 Ma then calibration is OK and carried out flushing of both impulse lines and gain take it in service it should read zero or 4 Ma.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bala
if the transmitter shows 4.5ma at zero pressure. we need to trim the tx by using hart communicator. there is an option in hart digital to analog trim. go to that option and make a trim and so if not D/A trim not proper then last need to replace the new transmitter.
Is This Answer Correct ? | 2 Yes | 0 No |
After the transmitter calibration they already fix the
transmitter on the prosces line. that time u check the
process line how mach pressure and check the 5 way manifold
condition and check the LP side impulseline chook. if its
ok manifold and impules line; open 5 way manifold equlizer
valve close any one hp or lp isolation valve that time tx
should be show zero 4ma. not showing 4ma. trim it zero.
zero not trimed cheange the transmitter.
Importent.
check the LRV how much its Zero Or not.
and check the wich type of transmitter.
if it is level transimtter that one different type of
callibration. check the where using the prossce line.
thank you
rajesh
Is This Answer Correct ? | 0 Yes | 0 No |
why we r opening HOT BYPASS valve during startup of a compressor?
Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?
What is the use of the shield wire and how is the connection at both the ends of a shield wire?
i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......
What are the most frequent problem faces with Vortex flow meter?
what is modbus,profibus,fieldbus
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
Why in turbine used two critical speed band ?
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
An engineering term STALL used in compressor operation what it means?
how can we caliberate interface level troll
2 Answers Grasim, IOCL, KOC, Sankyu,
How do you calibration D.P transmitter? ?