1 How to calculate dp transmitter
steam and water?
2 impulse line for liquid steam and
gas
Answer / carl_ellis
The DP pressure/flow transmitter is mounted above the pipe
for gas applications (empty impulse tubing).
The DP pressure/flow transmitter is mounted below the pipe
for liquid applications (liquid filled impulse tubing)
Steam flow applications using DP pressure transmitters were
historically mounted below-the-pipe (water filled impulse
tubing, frequently with condensate/seal pots), until
Emerson/Rosemount recently discovered that within certain
temperature limits, a DP transmitter close coupled on a
coplanar manifold to an Annubar averaging pitot tube can
survive steam temperatures mounted above-the-pipe.
See this link for Emerson's white paper on steam service
installation recommendations:
http://www2.emersonprocess.com/siteadmincenter/PM%
20Rosemount%20Documents/00870-0200-4809.pdf
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?
what is maximum vaccume?
2. What is ultrasonic flowmeter?
How we select the range of level transmitter in closed vessel ?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
What is the relationship between the universal gravitational constant (G) and the acceleration due to gravity (g)?
what is plc communication?
What is DCS and PLC scanning time?
this site is owned by an nonsense
Turbidity analyzer working principle ?
what can of fault ofently come in vibration mesurement?
How process line mpm calculation is done?