1 How to calculate dp transmitter
steam and water?
2 impulse line for liquid steam and
gas
Answer / carl_ellis
The DP pressure/flow transmitter is mounted above the pipe
for gas applications (empty impulse tubing).
The DP pressure/flow transmitter is mounted below the pipe
for liquid applications (liquid filled impulse tubing)
Steam flow applications using DP pressure transmitters were
historically mounted below-the-pipe (water filled impulse
tubing, frequently with condensate/seal pots), until
Emerson/Rosemount recently discovered that within certain
temperature limits, a DP transmitter close coupled on a
coplanar manifold to an Annubar averaging pitot tube can
survive steam temperatures mounted above-the-pipe.
See this link for Emerson's white paper on steam service
installation recommendations:
http://www2.emersonprocess.com/siteadmincenter/PM%
20Rosemount%20Documents/00870-0200-4809.pdf
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
How does milli volt is created in themocouple?
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
What is require for PLC Programming?
How to Calibrate Coriolis Flow transmitter in field
Explain why plc require in analog input 4-20amp & 0-10 volt?
What is Difference between PLC and CNC ?
what is modbus,profibus,fieldbus
Capacitance, resistance ( colour coding ), parallel & series circuits.
how the transmitter send MA?
Flame scanner
what is the differnce betweeen hart and smart tx
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)