why normally Generator rating are between 11Kv to 22Kv?
Answers were Sorted based on User's Feedback
Answer / vinod
Generator current depends on the power out put, if the
power is more current will be more.Sator current can be
reduced by increasing the genrator voltage, but there is
limit for increasing the voltage due to the insulation of
Stator ie. if the voltage is too high insulation level is
too thick and machine size will be too big and costlier.ie
why generation voltage is between 11 KV to 22 KV.
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ajay
You can have generation voltage less than 11kV like 3.3kV,
6.6kV etc but normally not more than 22kV because at higher
voltages rotor insulation at high speed is practically very
difficult to manage.
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / nithi
The power generation found more economical,when it is
generated in the voltage level upto 15kv.that's why the
generator in the power sector are rated upto 15kv.
| Is This Answer Correct ? | 11 Yes | 5 No |
Answer / raji g
in electrical power generation side they produce large
amount of power that means that generator windings carry
very large amount of current for low voltages like 440. if
we use 11kv the current in alternator windings is
reduced....hence usually high range of voltages are used in
power generation side
| Is This Answer Correct ? | 11 Yes | 7 No |
Answer / vinod singh
now a days power is generated by using powerformers in some
contries at higher voltage. in england on lule river power
is generated at 30KV . and ABB is also planning to
manufacture powerformer to generate powerat 45KV.
morover power is generated at 26KV in mundra by tatapower
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / ashok kumar gupta
ONE REASON IS GENERATOR CURRENT AND 22 KV CAN BE FED DIRECTLY TO THE LOAD FOR SMALL POWER REQUIREMENTS AND REDUCTION TO DISTRIBUTION TRANSFORMERS OF 11 KV WILL IMPROVE EFFICIENCY.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gaurav tripathi
because mostly power is generated between this voltage
| Is This Answer Correct ? | 7 Yes | 17 No |
how choose conductor&depending upon load
why we use 110vac in overhead crains? why not 220v, 24v
How to select HT/MV cable size ?
what is meant by armature reaction?
Why an ac systems are preferred over dc systems?
How to calculate Ith (I thermal) for curent transformer
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua
How to calculate 5hp 415v 3phase 2800rpm Ac motor full load current with out tourgh
In a 11KV 3phase system do you need to earth both sides of the cable?
What is the role of ESP(Electro Static Precipitator)in steam power plants? Where it is located? How it works?
Why dc shunt motor in lathe, compound motor in rolling mills
How Grading Rings & spacers in transmission lines works?working principle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)