why normally Generator rating are between 11Kv to 22Kv?
Answers were Sorted based on User's Feedback
Answer / vinod
Generator current depends on the power out put, if the
power is more current will be more.Sator current can be
reduced by increasing the genrator voltage, but there is
limit for increasing the voltage due to the insulation of
Stator ie. if the voltage is too high insulation level is
too thick and machine size will be too big and costlier.ie
why generation voltage is between 11 KV to 22 KV.
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ajay
You can have generation voltage less than 11kV like 3.3kV,
6.6kV etc but normally not more than 22kV because at higher
voltages rotor insulation at high speed is practically very
difficult to manage.
Is This Answer Correct ? | 23 Yes | 6 No |
Answer / nithi
The power generation found more economical,when it is
generated in the voltage level upto 15kv.that's why the
generator in the power sector are rated upto 15kv.
Is This Answer Correct ? | 11 Yes | 5 No |
Answer / raji g
in electrical power generation side they produce large
amount of power that means that generator windings carry
very large amount of current for low voltages like 440. if
we use 11kv the current in alternator windings is
reduced....hence usually high range of voltages are used in
power generation side
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / vinod singh
now a days power is generated by using powerformers in some
contries at higher voltage. in england on lule river power
is generated at 30KV . and ABB is also planning to
manufacture powerformer to generate powerat 45KV.
morover power is generated at 26KV in mundra by tatapower
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / ashok kumar gupta
ONE REASON IS GENERATOR CURRENT AND 22 KV CAN BE FED DIRECTLY TO THE LOAD FOR SMALL POWER REQUIREMENTS AND REDUCTION TO DISTRIBUTION TRANSFORMERS OF 11 KV WILL IMPROVE EFFICIENCY.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gaurav tripathi
because mostly power is generated between this voltage
Is This Answer Correct ? | 7 Yes | 17 No |
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
why HT wire making noise?
Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.
why earth wire is needed in a wiring system
What is the importance of Form B to state Electricity Boards?
What is the difference between newtral earthing and body earthing?
3 Answers JK Lakshmi Cement, NPCIL,
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
how a flip flop can be used as a latch?
What are the different modes of plc processor?
What is industrial automation ??????
In three phase energymeter the spindle rotating backward why?
we have 350 kva capcitor bank which is not showing KW. dose capacitor shows kW OR not.