Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Dear Sirs,
I am a technical persons.In one of our Electrical Sub-
Station, We have installed three numbers of
1250KVA ,11KV/0.415KV Transformer to feed the Factory load.
We have found some abnormality. In one of our Transformers
the leakeage current from transformer body to earth through
earth continuity wire is almost 86 Amp but in other
transformer it is (5-10)Amp. where the load current on
three phase and neutral are respectively
1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical
person help me about the reasons of this situation and how
I can rectify the fault. Moreover,I have measured the earth
resistance of the Earth continuity wire which is less than
1 Ohm.

Thanks

Tapas Barua

Answers were Sorted based on User's Feedback



Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three..

Answer / anadi biswas

Hi dear,
First of all tell me the condition
Are all these running parallel?If yes,then check the
individual winding to body insulation resistance with a
Multimeter.
Also you may check the transformer oil properties i.e.
dielectric strength as well in order ensure the minimum
leakages.

If individually connected , then check all the above+ the
nature of loads connected with the earthing system.
Also in all the above case check the body earthing of each
tranformer with Earth pits connected and individual earth
pits and measure the value. You will get the conclusion.

Is This Answer Correct ?    1 Yes 0 No

Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three..

Answer / sreenu

Hi dear,

Pls check the differential relay is not working properly, if its work this problem not faced. Pls check the primary current is equal to secondary current more than 30 times to the secondary winding.

Ex; if u have 2500kva transformer gives secondary current as per designing it vl gv 3477Amps is equal to primary current. Both r matches their is no problems transformer.

Is This Answer Correct ?    0 Yes 0 No

Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three..

Answer / k.prakashchandra

Check the insulation resistance of No. 1.Connect a voltmeter
between body and the earth and measure the leakage voltage
which is expected to be more 86V.Unbalanced currents are
also due to contact resistance .

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how

1 Answers  


PID controller details

1 Answers  


what is MAR

1 Answers   NCC,


What are the special protection given for high capacity Motor, more then 10mw

2 Answers  


what is reactive power?

8 Answers  


i want to syncronise 5 nos of DG. How? pls reply

3 Answers  


One 200 V, 100 W bulb is connected in series with primary of a 200 V, 10 kVA transformer. If its secondary is kept open circuited, then the bulb would have (1) Full brightness (2) Poor brightness (3) A little less than full brightness (4) More than full brightness...explain

2 Answers  


what is W.T?specify the acceptable range?

0 Answers  


I am an electrical engg and has got selected in wipro should i go there now or try in some core company ?

3 Answers   Wipro,


What type of a DC motor would you use for a lift?

0 Answers   GE,


why the India electrical supply transmission loss is high when compare to us

0 Answers  


i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)