Dear Sirs,
I am a technical persons.In one of our Electrical Sub-
Station, We have installed three numbers of
1250KVA ,11KV/0.415KV Transformer to feed the Factory load.
We have found some abnormality. In one of our Transformers
the leakeage current from transformer body to earth through
earth continuity wire is almost 86 Amp but in other
transformer it is (5-10)Amp. where the load current on
three phase and neutral are respectively
1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical
person help me about the reasons of this situation and how
I can rectify the fault. Moreover,I have measured the earth
resistance of the Earth continuity wire which is less than
1 Ohm.
Thanks
Tapas Barua
Answers were Sorted based on User's Feedback
Answer / anadi biswas
Hi dear,
First of all tell me the condition
Are all these running parallel?If yes,then check the
individual winding to body insulation resistance with a
Multimeter.
Also you may check the transformer oil properties i.e.
dielectric strength as well in order ensure the minimum
leakages.
If individually connected , then check all the above+ the
nature of loads connected with the earthing system.
Also in all the above case check the body earthing of each
tranformer with Earth pits connected and individual earth
pits and measure the value. You will get the conclusion.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sreenu
Hi dear,
Pls check the differential relay is not working properly, if its work this problem not faced. Pls check the primary current is equal to secondary current more than 30 times to the secondary winding.
Ex; if u have 2500kva transformer gives secondary current as per designing it vl gv 3477Amps is equal to primary current. Both r matches their is no problems transformer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Check the insulation resistance of No. 1.Connect a voltmeter
between body and the earth and measure the leakage voltage
which is expected to be more 86V.Unbalanced currents are
also due to contact resistance .
| Is This Answer Correct ? | 0 Yes | 1 No |
why transformer rating in kva and motor rating in kw
what is the difference between relay and a contactor.
Z transform is use when system is not a) converges b) diverges
Difference between mcband isolator
Why neutral cable carry current.
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
If we increases the %impedance of Transformer then price of Transformer will increases or decreases.
what is difference between line differential and transformer differential?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
how does a submersible pump work..?
How to work definite,over pluxing,revers power,OSR relay
What is contract demand in solar system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)