Dear Sirs,
I am a technical persons.In one of our Electrical Sub-
Station, We have installed three numbers of
1250KVA ,11KV/0.415KV Transformer to feed the Factory load.
We have found some abnormality. In one of our Transformers
the leakeage current from transformer body to earth through
earth continuity wire is almost 86 Amp but in other
transformer it is (5-10)Amp. where the load current on
three phase and neutral are respectively
1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical
person help me about the reasons of this situation and how
I can rectify the fault. Moreover,I have measured the earth
resistance of the Earth continuity wire which is less than
1 Ohm.
Thanks
Tapas Barua
Answers were Sorted based on User's Feedback
Answer / anadi biswas
Hi dear,
First of all tell me the condition
Are all these running parallel?If yes,then check the
individual winding to body insulation resistance with a
Multimeter.
Also you may check the transformer oil properties i.e.
dielectric strength as well in order ensure the minimum
leakages.
If individually connected , then check all the above+ the
nature of loads connected with the earthing system.
Also in all the above case check the body earthing of each
tranformer with Earth pits connected and individual earth
pits and measure the value. You will get the conclusion.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sreenu
Hi dear,
Pls check the differential relay is not working properly, if its work this problem not faced. Pls check the primary current is equal to secondary current more than 30 times to the secondary winding.
Ex; if u have 2500kva transformer gives secondary current as per designing it vl gv 3477Amps is equal to primary current. Both r matches their is no problems transformer.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Check the insulation resistance of No. 1.Connect a voltmeter
between body and the earth and measure the leakage voltage
which is expected to be more 86V.Unbalanced currents are
also due to contact resistance .
Is This Answer Correct ? | 0 Yes | 1 No |
what are the analog quality input for protection function?what are minimum reqiments?
What is mean CT Saturation? How to calculate?
how to check the LRS resistance .......................
why the pf of semiconductor device is improved the electrical devices
when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil
Is the force acting between two parallel conductors of infinte length carrying AC of frequency 50Hz remians constant with respect of time? If not then what would be the frequency of the force acting?
what is the difference between contactors & relay.
in dc machines in the armature nature of power is ac but why we take rasistance instead of impedance?
difference between temperature sensor and temperature switch
explain impact of tariff on energy management..? and what is ABT tariff
how to find under ground cable fault ??? if our cable size is 95*4 then what will load capacity with far mull
When both contractor star & delta is hold in star delta motor ?? So what happen in this case ??