Three phase alternators are connected in star connection
why?
Answers were Sorted based on User's Feedback
Answer / ashna & anju
in star conection ,phase voltage is lesser than line
voltage and induced emf in the phase winding of an
alternator is directly propotional to number of turns,a
star connected alternator will require less number of turns
than a delta connected one for the same line voltage.
| Is This Answer Correct ? | 68 Yes | 10 No |
Answer / $$$
TTT
IT IS BECAUSE THIRD HARMONICS CAN BE ELIMINATED USING STAR
CONNECTION AND DISTRIBUTED WINDINGS IN 3-PH ALTERNATORS..
| Is This Answer Correct ? | 36 Yes | 14 No |
Answer / ajay
IT IS BECAUSE THIRD HARMONICS CAN BE ELIMINATED USING STAR
CONNECTION AND DISTRIBUTED WINDINGS IN 3-PH ALTERNATORS..
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / muhammed konikkal
out put is required in AC form with neutral.Neutral can be taken only from Star connection. We can take out put single phase or three phase depending our load.
| Is This Answer Correct ? | 8 Yes | 7 No |
in a star connection, phase voltage Vph = VL/ (3)^1/2.
1--Since the induced emf in the primary winding of an alternator is directly proportional to the number of turns, a star connected alternator will require less number of turns than a delta connected alternator for the same voltage.
2-- it also requires less insulation bcz its phase is less.
3-- it also help to reduce third harmonic ...
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / sudheer
induce emf is proportional to turns so for same line voltage no of turns required is less hence insulation required is less and for protectio purpose we require ground so ground provided in case of star only
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / binod pradhan
2-in star connection the phase voltage is low than the line voltage,so it required less no of turn. 3-low insulation required as phase voltage is low. 4-1 neutral point available in star connection. 5-unbalance current flowing in the three phase circuit, neutral is having a vital role.It will take the unbalance current through to the ground.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mahfooz alam
In Star connection the Line Voltage is 1.732 times the phase voltage. As a result of which we can have the higher voltage in star connection when compared to the delta connection. Thus, to have more output voltage Star connected Alternator are used.
| Is This Answer Correct ? | 6 Yes | 12 No |
how can we measure the import power and export power in the same line?
If 110V DC Coil Contactor taken 15ma DC on load,than how much AC current wil be taken?
0 Answers Lafarge, Shree Cement,
What do you mean by isolators and circuit breakers?
6 Answers Bhushan Power Steel,
why diesel tank is earthed
What is Goerges phenomina to start SYCHNOUSMOTOR?
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
EXPLAIN THE ESSENTIAL FACTORS WHICH INFLUENCES THE CHOICE OF SITE FOR A HYDRO ELECTRIC POWER PLANT
difference between a four point starter and three point starter
in 132kv substation CRT means
what is inverter and converter
7 Answers Shrishti Power Technologies,
Cummins 750 KVA generator how much disel consumed per hour and how many units generated on 100% full load.
The electromagnetic torque developed is proportional to what in a D.C series motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)