Cummins 750 KVA generator how much disel consumed per hour
and how many units generated on 100% full load.
Answer / chintu
Generally Diesel Gen sets consume fuel economically at 75% of full load @ 0.2 lts per kVA per hour( strictly speaking @ 145 gms/BHP/Hr). 750*0.2= 150 lts per hour.
| Is This Answer Correct ? | 15 Yes | 6 No |
Upto what extent, the lagging power factor can be improved with the help of capacitors?
How to calculate the size of the conductor for particular load
what will happen if we double the input frequency of a transformer keeping the voltage constant?
What are the types of transformers according to the arrangement of iron cores?
I have AC automatic voltage regulator 15KVA What output currant?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
what happens when ac supply is given to D.C motor.
why voltage ratings of xmission are in 11, 33,66kv and why not 11.5 ,16,19 or any other
why the electrolyte level in lead acid battery is maintained 2.5 cms above electrodes?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
What is the difference between a fuse and a breaker?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)