Cummins 750 KVA generator how much disel consumed per hour
and how many units generated on 100% full load.
Answer / chintu
Generally Diesel Gen sets consume fuel economically at 75% of full load @ 0.2 lts per kVA per hour( strictly speaking @ 145 gms/BHP/Hr). 750*0.2= 150 lts per hour.
Is This Answer Correct ? | 15 Yes | 6 No |
why measure the gravity in battery?
How to design pavement quality concrete by using C.R.C.P Method
which type of starter is suitable for single phase motor ?
why the transformer ratings in kva
Hi, I'm running plastic reprocessing company where all motors are running only in delta. Due to that when I use start my 30 hp motor my transformer gets fuse. Where it happens two times a day. I gt a suggestion from a person about Automatic Power Factor Controller APFC. Is it useful for my problem??? Or is der any other way for solving this problem?? Upgrading the transformer is difficult. Pls give Me ur suggestion. Waiting for ur reply.
2 Answers Shree Lingaa Polymer,
what does the regenerative braking mean?and how it used for Dc motor? thanks.
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
how to reduce humming noise in transformer?
is earthing is necessary if we use armoured cable
1 Answers ABB, Schwing Stetter, Siemens,
Welding machine
On wat basis TSM & PSM are set? Example.TSM=30% n PSM=2.5A....Hw they are set and how we come to know that the particular relay should be set to this value only?
How I can Compare 120v/60Hz versus 220v/50Hz ? Please tell me both advantage and disadvantage ......