Fault current shall be part of tech specs of power cable or not?.
Answer / viren89desai@yahoo.co.in
During a short circuit, a high amount of current can flow through a cable for a short time. This surge in current flow causes a temperature rise within the cable. High temperatures can trigger unwanted reactions in the cable insulation, sheath materials and other components, which can prematurely degrade the condition of the cable. As the cross-sectional area of the cable increases, it can dissipate higher fault currents for a given temperature rise. Therefore, cables should be sized to withstand the largest short circuit that it is expected to see.
http://www.openelectrical.org/wiki/index.php?title=Cable_Sizing_Calculation
| Is This Answer Correct ? | 0 Yes | 0 No |
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
why substation ratings are multiple of 11 means 11\33 kv substation
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
Please send specifications for 1000KVA dry type transformer or where I can get the specifications?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
what is the definition of a power transformer ?
how to calculate the multiplying factor for energy meter with CT ratio given
23 Answers Bhel, Dalmia Group, DIFC, Fedco, Hindustan Unilever Limited, Lupin, MahaDiscom, MAL Pakistan, Myunghwa Automotive, Panchshil Infrastructure, Regala, RVPN, VIPL,
what is the meaning of "i.p.-43" and duty cycle-s1 on the name plate of a asynchronous machine?
Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?
Is it any dc fuses availbale in market? can we use one fuse for both AC & DC ?
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
What is mean by diversity Fator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)