Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why generally the Rating of Transformers are in additions
of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........

Answers were Sorted based on User's Feedback



Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / p. h. godavary

Here the question is not correct. Transformer ratings are never in multiples of 11.

It is the Generator voltages that are in multiples of Form factor 1.1(approx.). The voltages are 3300V, 6600V, 11000V. Consequently the normal distribution / transmitting voltages used are 3.3KV, 6.6KV, 11KV, 33KV, 66KV 110KV, .......

Form factor of an alternating current waveform is the ratio of the RMS (Root Mean Square) value to the Average Value of the waveform]. In the case of a sinusoidal wave i.e. , an analogue wave, the form factor is approximately 1.11

Is This Answer Correct ?    34 Yes 3 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / bharathi

Due to form factor...
The value of form factor is 1.141
So, thats y the rating of transformers r in multiples of
form factor..

Is This Answer Correct ?    18 Yes 5 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / ms.gayathri

The rating of transformer is always not in multiples of 11
i.e., the voltages are only in multiples due to the form
factor. Form factor is nothing but the physical size and
shape of a device. Which is approximately 1.11 derived from
the ratio between RMS value and Average value of the sine
waveform(analog).

Is This Answer Correct ?    11 Yes 2 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / ali

Dears question is why in addition of 11.... that is 22 ..33

Is This Answer Correct ?    8 Yes 14 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / amjad

Due to form factor...
The value of form factor is 1.723
So, thats y the rating of transformers r in multiples of
form factor..

Is This Answer Correct ?    8 Yes 17 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / arun

in above of that rating of transformers only will have very
less harmonics...when compare with other rating...

Is This Answer Correct ?    5 Yes 18 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / denish konsam, manipur

Because the load on the transformer depends upon the power
factor. If it is given in KW then the load will be fixed
that means that transformer can be used for only one load.

Is This Answer Correct ?    6 Yes 25 No

Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc....

Answer / abdul wajid

Basically there are two type of losses in Transformer Iron
losses and core losses Iron losses depend upon voltage and
core losses depends upon current so the total losses
depends upon voltage and current hence transformer ratin is
taken as KVA

Is This Answer Correct ?    11 Yes 50 No

Post New Answer

More Electrical Engineering Interview Questions

Technical specification of a wind farm

1 Answers  


Excat meaning of burden in only one word?

3 Answers   Bhel, DG Electricals,


How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.

0 Answers  


How test for Ddo vector group test condition?

0 Answers  


If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a campus site?

2 Answers  


how on load transformer is chnage the Tapping ?

2 Answers  


what is the effect of higher value of GD???

0 Answers   VEPL,


why ligthing is not available in switch yards?

1 Answers  


Why you want to join non technical field when you are an engineer?

0 Answers  


why full load voltage is less than no load voltage?

4 Answers  


What are the different condition monitoring techniques for a motor?

1 Answers   DAE,


does buccholz in a transformer use batteries

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)