how do you measure earth leakages in 3phase wires?
Answers were Sorted based on User's Feedback
Answer / tim
typically this can be done using a high potential device
that applies a high voltage signal to open circuited
conductors. The meter on the device measure the micro-amps
of leakage through the insulation of the cables.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sapan sahni
We can check earth leakage by a instrument Its name is Magger.
| Is This Answer Correct ? | 1 Yes | 3 No |
what is IP 55 & IP 54 ?
What is Peterson coil? Where it is used?
What is the clear distance between a MV panel(rear side) and wall.
how you can select circuit breaker for 2000kva transformer?
Why derivative controller is not used in control systems?
What are effect of radio system in DCS Distributed control system ?
diff between synchronous gen and alternators
In the market there is availability of MCCB & ACB (800A), So, Where i can use MCCB & ACB for the same Rating?
What will be the full load current of 60KVA UPS. Suggest for this formula.
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
What does Magnetic Neutral Axis
2 Answers Eskom, Genus, Lanco,
What is the application of Nitrogen Injection system in Transformer Protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)